Correct, and that is helpful.   A lot depends on the sprink/piping layout.    
As others have pointed out, the difference in pipe size normally isn’t much.  
Just finished a project where the main down the corridor had to be 2.5” to make 
residential sprinks work.  Was able to reduce it to 2” when we switched the 
design to QR.   The primary reason was back-to-back sidewall sprinks in the 
demising walls combined with a marginal water supply – if the water supply had 
been better, a 2” main would have worked for the residential sprinks also.  
Just another tool to have in the toolbox.

 

Ed Kramer

Bamford Fire 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Wednesday, March 01, 2017 10:51 AM
To: [email protected]
Subject: Re: Dwelling Unit Sprinkler Calc

 

You can use small room rule and do room area divided by number of heads to get 
0.1 flow. Then compare that to data sheet. 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Mar 1, 2017, at 9:43 AM, Ed Kramer <[email protected] 
<mailto:[email protected]> > wrote:

I agree – 4 heads regardless of walls, even if the walls are rated.  It creates 
a bit of a penalty when using residential sprinks.  I understand the reasoning 
back when we didn’t provide a .10 density, but not so much now.   Sometimes 
I’ve found it’s more economical to switch to QR sprinks and then utilize the 
room design method.  Just depends on the particulars of your layout.

 

Ed Kramer

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Wednesday, March 01, 2017 10:17 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: Re: Dwelling Unit Sprinkler Calc

 

It is regardless of walls. I pick 4 on one line if they are the most demanding. 
If unsure, just throw on a few calc areas and take the most demanding one. 
(Another plug for Autosprink - draw the extra remote areas. Tell it to keep 
most demanding and you are done). 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Mar 1, 2017, at 9:05 AM, Dewayne Martinez <[email protected] 
<mailto:[email protected]> > wrote:

NFPA 13 (10) section 11.3.1.1 also includes “adjacent”.  What does this mean 
actually?  4 heads on the same line regardless of the walls or 4 heads in the 
same area but may be supplied from different lines?  The pictures in the 
appendix are not very clear.

Thanks,

Dewayne

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of 
[email protected] <mailto:[email protected]> 
Sent: Friday, July 08, 2016 9:13 AM
To: sprinklerforum
Subject: Re: Dwelling Unit Sprinkler Calc

 

In response to the original question, is it just me or are we over-thinking 
this?

NFPA 13 says that when using residential heads, you calculate the 4 heads that 
produce the greatest hydraulic demand.  No mention of units, rated walls, 
corridors, type of construction, etc.

 

I didn't know George Church, but I would have liked him.

 


  _____  


From: "Travis Mack" <[email protected] <mailto:[email protected]> >
To: [email protected] <mailto:[email protected]> , "sprinklerforum" 
<[email protected] 
<mailto:[email protected]> >
Sent: Tuesday, July 5, 2016 3:44:35 PM
Subject: Re: Dwelling Unit Sprinkler Calc

 

I'd probably grab the adjacent sprinkler in the adjacent room. 

 

 

 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Jul 5, 2016, at 12:34 PM, Bob <[email protected] 
<mailto:[email protected]> > wrote:

 

I have a NFPA 13 building with Dwelling Units.  They each have three 
Residential Sprinklers.  13 requires a four head calc.  Can I calc the 3 
residential sprinklers and pick up one QR sprinkler in the corridor and still 
satisfy the 4 head requirement?  Or, should I pick up one residential sprinkler 
from an adjacent dwelling room?

 

Thank you,

 

Bob Knight, CET III

208-318-3057

<image002.jpg>

 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to