Even though there is a half-wall is separating the two as long as the office 
has a ceiling two different K factors

is acceptable.


I do numerous facilities where there are ESFR sprinklers at the roof with 
tenant offices below with suspended

ceilings only, K 5.6 for the office and ESFR's at the roof is acceptable.


Mike


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Tim Easter <[email protected]>
Sent: Thursday, March 2, 2017 8:58 AM
To: [email protected]
Subject: different k-factors in same area


I have a half-wall that separates an office area from a warehouse area. The 
design is for K factors of 8.0 inside warehouse area, and 5.6 inside office 
area. But since the halfwall doesn’t reach the deck the area above the office 
area protected from the ceiling  must have same k-factor as warehouse correct? 
Can anyone point that out in NFPA 13 as a code reference?







Tim Easter, PE

[Description: Description: Description: 
http://www.wwgfp.com/MailLogo.gif]<http://www.wwgfp.com/Brochere.jpg>

[http://www.wwgfp.com/Brochere.jpg]

522 Stockton Street

Jacksonville, FL 32204

Office: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261











     This electronic message contains information from W. W. Gay Fire 
Protection, Inc., which may be confidential or privileged. The information is 
for use of the individual or the entity named above. If you are not the 
intended recipient, please be aware that any disclosure, copying, distribution 
or use of the contents of this message is prohibited. If you have received this 
electronic transmission in error, please notify us immediately at 
1-904-387-7973.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to