People often get this confused. You can't use smaller k-factors to balance the 
system calcs. For example you can't have K8 at the end of a line, then 5.6 in 
the middle and 4.2k adjacent to the main. This would be done to reduce over 
discharge. 

This is not what you are doing. It is no different than having extended 
coverage and standard coverage in the same room. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Mar 2, 2017, at 7:16 AM, Charles Thurston <[email protected]> wrote:
> 
> Hello Tim,
> 
> I don't have the book in front of me, but no the K factor does not have to be 
> the same. It calls for the same temperature heads in the same area. K factors 
> are different in a lot of rooms for different coverage areas.
> 
> 
> Thursday, March 2, 2017, 8:58:02 AM, you wrote:
> 
> 
> I have a half-wall that separates an office area from a warehouse area. The 
> design is for K factors of 8.0 inside warehouse area, and 5.6 inside office 
> area. But since the halfwall doesn’t reach the deck the area above the office 
> area protected from the ceiling  must have same k-factor as warehouse 
> correct? Can anyone point that out in NFPA 13 as a code reference?
> 
> 
> 
> Tim Easter,PE
> <int_1.jpg>
> 522 Stockton Street
> Jacksonville, FL 32204
> Office: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261
> 
> 
> 
> 
> 
>     This electronic message contains information from W. W. Gay Fire 
> Protection, Inc., which may be confidential or privileged. The information is 
> for use of the individual or the entity named above. If you are not the 
> intended recipient, please be aware that any disclosure, copying, 
> distribution or use of the contents of this message is prohibited. If you 
> have received this electronic transmission in error, please notify us 
> immediately at 1-904-387-7973.
> 
> 
> 
> -- 
> Best regards,
> Charles Thurston                          [email protected]
> MYRTLE BEACH FIRE SAFETY GROUP
> A Division of Pye-Barker Fire Safety
> 1445 Cannon Road
> Myrtle Beach, SC 29577
> (843) 916 - 8787
> (843) 839 - 3473 facsimile
> 
> <int_2.jpg>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to