People often get this confused. You can't use smaller k-factors to balance the system calcs. For example you can't have K8 at the end of a line, then 5.6 in the middle and 4.2k adjacent to the main. This would be done to reduce over discharge.
This is not what you are doing. It is no different than having extended coverage and standard coverage in the same room. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Mar 2, 2017, at 7:16 AM, Charles Thurston <[email protected]> wrote: > > Hello Tim, > > I don't have the book in front of me, but no the K factor does not have to be > the same. It calls for the same temperature heads in the same area. K factors > are different in a lot of rooms for different coverage areas. > > > Thursday, March 2, 2017, 8:58:02 AM, you wrote: > > > I have a half-wall that separates an office area from a warehouse area. The > design is for K factors of 8.0 inside warehouse area, and 5.6 inside office > area. But since the halfwall doesn’t reach the deck the area above the office > area protected from the ceiling must have same k-factor as warehouse > correct? Can anyone point that out in NFPA 13 as a code reference? > > > > Tim Easter,PE > <int_1.jpg> > 522 Stockton Street > Jacksonville, FL 32204 > Office: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261 > > > > > > This electronic message contains information from W. W. Gay Fire > Protection, Inc., which may be confidential or privileged. The information is > for use of the individual or the entity named above. If you are not the > intended recipient, please be aware that any disclosure, copying, > distribution or use of the contents of this message is prohibited. If you > have received this electronic transmission in error, please notify us > immediately at 1-904-387-7973. > > > > -- > Best regards, > Charles Thurston [email protected] > MYRTLE BEACH FIRE SAFETY GROUP > A Division of Pye-Barker Fire Safety > 1445 Cannon Road > Myrtle Beach, SC 29577 > (843) 916 - 8787 > (843) 839 - 3473 facsimile > > <int_2.jpg> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org