I see it as no different than if you have a 2 story volume in an office and the rest is 9'. Calculate the space based on the QR reduction. Then, calculate the space around the higher ceiling at 1500 sq ft or whatever the reduction may be.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 3/31/2017 8:22 AM, Matt Grise wrote:

We are looking at a dry parking garage that has mostly flat ceilings. In one small area the ceiling slopes greater than 2 in 12 as part of the ramp that goes up/down. Is it acceptable to calculate one area of 2535 SF for any locations that include or are next to the sloped space, but then go to the flat spaces and calc 1950? I was not sure if that counted as an adjacent hazard? It seems both different and similar.

The lesser operating area allows for pipe to be sized smaller thus reducing dry volume and pipe cost.

What does the forum think?

**we decided to go all 2535 sf operating area throughout the garage. On a quick look, the pipe savings would not make up for the added design effort (some 1.5” went to 1.25”). I thought it was an interesting question though. Has anyone out there come across a similar situation?

Matt



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to