You are allowed as many design basis within one system as you see fit. Look at 11.1.1 - A building OR PORTION THEREOF shall be permitted ….. IT does does design approach but even within one approach (aka area/density) you can have multiple design basis.
Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Mar 31, 2017, at 8:22 AM, Matt Grise <[email protected]> wrote: > > We are looking at a dry parking garage that has mostly flat ceilings. In one > small area the ceiling slopes greater than 2 in 12 as part of the ramp that > goes up/down. Is it acceptable to calculate one area of 2535 SF for any > locations that include or are next to the sloped space, but then go to the > flat spaces and calc 1950? I was not sure if that counted as an adjacent > hazard? It seems both different and similar. > > The lesser operating area allows for pipe to be sized smaller thus reducing > dry volume and pipe cost. > > What does the forum think? > > **we decided to go all 2535 sf operating area throughout the garage. On a > quick look, the pipe savings would not make up for the added design effort > (some 1.5” went to 1.25”). I thought it was an interesting question though. > Has anyone out there come across a similar situation? > > Matt > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org