If I'm understanding
The roof system is unchanged and your adding a lower supply to be rooms.

Use standard qr heads and same pipe sizes

The roof is still most demanding

Sent from my Verizon 4G LTE Droid
On Apr 6, 2017 9:14 AM, Dewayne Martinez <[email protected]> wrote:
NFPA 13 (07ed)

I have an existing 5th floor shell space that is installed as a light hazard 
dry system that has pipe in the shell space and in the attic.  They are turning 
this floor into a dormitory (R-2).
1)Can I use listed residential heads on return bends and only pick up 4 heads 
per 11.3.1.1 or will I need to pick up 1950SF?  What if there are incidental 
areas such as a laundry room, ect. in the same areas as the dorm rooms?
2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for 
residential or 60sec for light hazard?