The only time I've seen this was a four story assisted living facility. Each 
floor used different pipe sizes, and there were at least two different spacing 
of heads in hallways on different floors.

I wondered if smaller pipe, and ftgs, vs speed of install, i.e. labor expense, 
paid out. Of course that wasn't my business so I never knew answer to that 
question.

Best 

Bruce Verhei 

> On Apr 12, 2017, at 10:08, Travis Mack, SET <[email protected]> wrote:
> 
> The wording in the newer editions of NFPA can be interpreted that each floor 
> is required to have calculations.  I have not had anyone enforce it yet, but 
> am just waiting for it to happen.  I typically do as you do.
> 
> I use my BOR demand at the gauge on the floor control valve.  So, for a 
> demand calc, your pressures / flows are not going to change if that is the 
> point you use as your BOR for your calc tags. As long as all pipe sizes are 
> the same, pipe routing, etc.. Then the demand is the same at the floor gauge. 
> Now, if you were doing a supply calc, then you would have different numbers.
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
> 
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign 
> LinkedIn: https://www.linkedin.com/in/travismack
>> On 4/12/2017 10:04 AM, Jerry Van Kolken wrote:
>> Often I do a multi-story building with typical floors. So I only provide a 
>> calculation on the top floor and first floor due to a higher hazard area. At 
>> the end of the job we are asked to provide calc. plates for every floor. I 
>> will just copy the typical floor information down, but I know the pressures 
>> will be incorrect as I move down the building.
>>  
>> Is there a requirement for this?
>>  
>> Jerry Van Kolken
>> Millennium Fire Protection Corp.
>> 2950 San Luis Rey Rd.
>> Oceanside, CA 92058
>> (760) 722-2722 FX 722-2730
>>  
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to