Is what you're referring to the Captive Aire's CORE fire suppression system?  
https://www.captiveaire.com/catalogcontent/firesuppression/core/index.asp


Interesting system for cleaning and suppression.  It uses water combined with a 
surfactant to make it work.

Apparently it is ETL listed to UL 300 standards and meets criteria of NFPA 17A 
(wet chemical extinguishing systems) and NFPA 96.

Looks like it can be tied into plumbing systems or building sprinkler system.  
So what NFPA language would prevent this from being connected to the sprinkler 
system?



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Thursday, April 20, 2017 2:33 PM
To: [email protected]
Subject: RE: Hood System - Question [EXTERNAL]

I don't have the exact model yet but the manufacturer is Captive Aire. I meant 
approved/listed in the sense "as a hood system" not as a part of a fire 
sprinkler system.



Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 20, 2017 2:28 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question

You say it's "approved and listed".  If that is the case, why would it not be 
allowed?

Do you have a link to this unit?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Thursday, April 20, 2017 2:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Hood System - Question [EXTERNAL]

Good afternoon all,

Apparently, there is a standalone approved/listed type of hood suppression 
system for kitchens that uses water as the extinguishing agent. Within their 
data sheet it states that it requires a supervised water source "or" that it 
may be tied into the fire sprinkler system. It has a minimum required starting 
water pressure of 30psi and "IF" it is supplied/tied into the sprinkler system 
then it would most definitely have to be accounted for in the hydraulics. But, 
it is obviously not a part of the fire sprinkler system or NFPA 13. My first 
thought is that regardless of their data sheet, it shouldn't be allowed per 
NFPA 13. Am I thinking correctly? Wouldn't it be considered a non-system 
component and not allowed?


[USBR Best of USA 2016_rev2]


Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to