It is another contractor providing the hood system. Our system is already 
designed, permitted, installed and inspected. They are trying to get a building 
final (and hood final) within a week and the hood contractor just now brings up 
the fact he needs water.

Thank you to everyone for the responses. At this point it's not really our 
problem. I would agree that they could tie into the underground/riser below the 
control/check valve as a "separate system", but we don't want it tied into the 
overhead. The system was not calculated for the additional psi/flow and as was 
said the cleaning cycle would trigger flow alarms.




Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703



Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 20, 2017 3:31 PM
To: [email protected]
Subject: RE: Hood System - Question

The Piranha system is only fire suppression.  This system has multiple 
functions where it is a cleaning system AND a fire suppression system.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Williams
Sent: Thursday, April 20, 2017 3:27 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question [EXTERNAL]

How is this different than an Ansul Piranha system (as far as the connection to 
the sprinkler system?). We are required to use something like the Piranha in 
some jurisdictions so the system continues to function after the agent is gone 
(same thing for Clean Agent.. must have 20-60 minute duration). Or any other 
pre-piping that can be supplied by the kitchen hood manufacturers?

Is it that some other contractor is supplying the equipment?

David Toshio Williams, PE/FPE, LEED-AP O+M
(218) 279-2436 direct | (218) 310-2446 cell
LHB, Inc. | PERFORMANCE DRIVEN DESIGN



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: Thursday, April 20, 2017 2:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question

We have run into that before in large hotels etc.
Its for FIRE protection so people assume that sprinkler contractor will be 
tying into it.
We always push back and have the plumbing contractor supply to it.

Do so by  saying if it connects to the fire sprinkler system there needs to be 
a valve and that valves needs to be monitored and then it snowballs into  its 
just easier for plumbing to add it as if was a ice machine etc.

IMHO

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Thursday, April 20, 2017 3:05 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question

Yes that is it, first time ever seeing it and my initial thought was it's not 
part of the sprinkler system and I couldn't find any guidance in NFPA 13 about 
non-system connections that discharge water. Section 7.7 addresses connections 
for heating and cooling but clearly state there can be no water discharge from 
those auxiliary systems.



Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 20, 2017 2:50 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question

Is what you're referring to the Captive Aire's CORE fire suppression system?  
https://secure-web.cisco.com/19ZHcCEdUbGNfvY7uSLHExQ6pGIhbtrzMy0OK4K2ihL_cNtZMRdYyPizCHvuB6LcmEPVxaGv5dYr3LFSbjgqBg0JUn7JUPw78Ef43xJeG2ee9XNsWS7vyTWx3fXdioVF8GeVm3Vje7x21YaG19boE-3j9KbFa7mRXWNe-5p1ZFT5jTFaQRe4TILQrMJsPsMpKtRQzqS06Psanwbq7DdX9x-ebpEooS3JsqwbEQv1jHwZ-xPw0cUHkUQygnFWO_WGKvbE0IXVxoUv38uIPojYHOuBTDF8-F5BYw8Y3JEW0rsk6YM7k_-zzTLNYbeK2Csz1EHiNYV6czWRwxYYGxJ-AhXfcSLf0fVg7mHVyXpvdo4J28Q9GHkUjkKDNudd2zCNOaFb-9Feuaui5EeQSKsmGx6n3sW1G59rwS7xC3PdcKB0DU9sult5kZ8ocRwLhPcodtHrx7Yqm9ozqvowQk60__rD6Qr3kMvoUd_2Wm8KCKTk/https%3A%2F%2Fwww.captiveaire.com%2Fcatalogcontent%2Ffiresuppression%2Fcore%2Findex.asp


Interesting system for cleaning and suppression.  It uses water combined with a 
surfactant to make it work.

Apparently it is ETL listed to UL 300 standards and meets criteria of NFPA 17A 
(wet chemical extinguishing systems) and NFPA 96.

Looks like it can be tied into plumbing systems or building sprinkler system.  
So what NFPA language would prevent this from being connected to the sprinkler 
system?



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Thursday, April 20, 2017 2:33 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question [EXTERNAL]

I don't have the exact model yet but the manufacturer is Captive Aire. I meant 
approved/listed in the sense "as a hood system" not as a part of a fire 
sprinkler system.



Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 20, 2017 2:28 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Hood System - Question

You say it's "approved and listed".  If that is the case, why would it not be 
allowed?

Do you have a link to this unit?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Eric V. Tysinger
Sent: Thursday, April 20, 2017 2:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Hood System - Question [EXTERNAL]

Good afternoon all,

Apparently, there is a standalone approved/listed type of hood suppression 
system for kitchens that uses water as the extinguishing agent. Within their 
data sheet it states that it requires a supervised water source "or" that it 
may be tied into the fire sprinkler system. It has a minimum required starting 
water pressure of 30psi and "IF" it is supplied/tied into the sprinkler system 
then it would most definitely have to be accounted for in the hydraulics. But, 
it is obviously not a part of the fire sprinkler system or NFPA 13. My first 
thought is that regardless of their data sheet, it shouldn't be allowed per 
NFPA 13. Am I thinking correctly? Wouldn't it be considered a non-system 
component and not allowed?


[cid:[email protected]]


Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL

Email: [email protected]<mailto:[email protected]>
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703





Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use of the 
intended recipients and may contain confidential and privileged information. 
Any unauthorized review, use, disclosure or distribution is prohibited. If you 
are not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to