IBC requires balconies to be protected for 13R systems where there is Type V construction. This doesn't apply here as 1) you have a 13 design and 2) you have non-combustible construction. You should be good to omit the sprinklers per 8.15.7.
Micah Davis Dynamic Fire Designs www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com> ________________________________ From: Sprinklerforum <[email protected]> on behalf of John Irwin <[email protected]> Sent: Friday, April 21, 2017 8:19 AM To: [email protected] Subject: Sprinkler Protection on Balconies High-rise Condo Building. Non-combustible construction. I refer to 8.15.7.1 which points me to 8.15.7.2. If I meet the requirements of 8.15.7.2, can I stop reading and omit the sprinklers on the balcony? Specifically, the penthouse level balconies have outdoor kitchens. It’s been questioned whether or not these are required to be protected. I can’t find anything in NFPA 101, the Florida Fire Prevention Code or the Florida Building Code that would be more restrictive than 8.15.7.2 I say the sprinkler protection is not required, outdoor kitchen or not. Comments? [cid:[email protected]] John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC License Number: FPC16-000053 2830 Scherer Drive, Suite 300 St. Petersburg, FL 33716 Office: 727.209.5122 Fax: 727.209.5126 Cell: 813.618.2781 Email: [email protected]<mailto:[email protected]>