IBC requires balconies to be protected for 13R systems where there is Type V 
construction.  This doesn't apply here as 1) you have a 13 design and 2) you 
have non-combustible construction.  You should be good to omit the sprinklers 
per 8.15.7.


Micah Davis

Dynamic Fire Designs

www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com>


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of John Irwin <[email protected]>
Sent: Friday, April 21, 2017 8:19 AM
To: [email protected]
Subject: Sprinkler Protection on Balconies


High-rise Condo Building. Non-combustible construction.  I refer to 8.15.7.1 
which points me to 8.15.7.2. If I meet the requirements of 8.15.7.2, can I stop 
reading and omit the sprinklers on the balcony? Specifically, the penthouse 
level balconies have outdoor kitchens. It’s been questioned whether or not 
these are required to be protected. I can’t find anything in NFPA 101, the 
Florida Fire Prevention Code or the Florida Building Code that would be more 
restrictive than 8.15.7.2



I say the sprinkler protection is not required, outdoor kitchen or not.



Comments?