Ladies/Gentlemen:
 
I am not a committee Member. But my position as a Fire  Protection Engineer 
would be NOT to replace "shell" sprinklers with QR UNTIL new tenants occupy 
space(s) and determine if they are LH or OH/XH...My  co-workers (retired 
State Fire Marshals) concur. If I were the AHJ, I would rule  'leave them in 
place', as is, until occupied, then make  determination.
 
Best to All-
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, M.S.F.P.E.
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961 nationwide
 
*Licensed Architects - Fire protection Engineers/NICET  Designers/NICET 
Inspectors/Forensics/Fire Investigators: AZ  CA   CO  NM  NV  NY  TX  UT  KS  
MD   MS
 
 
 
 
In a message dated 6/1/2017 4:06:23 P.M. Mountain Daylight Time,  
[email protected] writes:

 
Question for all my NFPA 13 committee members (and anyone  else who wants 
to chime in).  We have (4) building that have had the  offices and ceilings 
demolished leaving it a market ready warm shell. AHJ is  now stating that all 
existing uprights need to be removed  and replaced  with QR sprinklers.  
A.8.3.3.1 states ”when renovations occur in an  existing building and no 
changes are made in the existing sprinkler system,  this section is not 
intended 
to require the replacement of existing standard  response sprinklers with 
quick-response sprinklers”  does  the removal of the existing drops due to the 
removal of the ceiling  constitute “changes made to the existing system” 
??  My feeling is  this wasn’t the intent of the committee (and I’m probably 
wrong)  but  I’d like to hear everyone’s comments/thoughts.  
Thank you!! 
Rocci  Cetani III, CET 
Senior  Designer 
Water-Based Fire Protections Systems Layout, Nicet Level  III 
Northern  California Fire Protection Services Inc. 
16840 Joleen Way Bldg.  A 
Morgan Hill, CA  93037 
P-(408) 776-1580  EXT.111 
F-(408)  776-1590 
[email protected]_ (mailto:[email protected])  
_www.norcalfire.com_ (http://www.norcalfire.com/)  
CONFIDENTIALITY  NOTICE: This message and any document accompanying it may 
contain confidential  information  
belonging to the  sender. The information is intended only for the use of 
individual or entity  named above. If you are not the intended recipient, or 
the employee or agent  responsible to deliver this message to the intended 
recipient, you are hereby  notified that any disclosure, copying or taking of 
any action in reliance on  the contents of this information is strictly 
prohibited. If you have received  this transmission in error, please 
immediately notify us by telephone to  arrange for return of the documents. 



_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to