We had a similar situation (but 4-5") where raising the ceiling was not an 
option for structural reasons. In that case they enclosed the space above the 
simulator creating a n/c space which didn't require sprinklers. We did not put 
protection inside the simulator. See if the unit needs ventilation and look at 
how they are handling that.   
    
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-553-3553 (tel:860-553-3553)  (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  
  

  
  
>   
> On Jun 8, 2017 at 9:53 AM,  <Dewayne Martinez 
> (mailto:[email protected])>  wrote:
>   
>   
>       
>   
>
> I have a room with a 10’2” ceiling where a self-contained golf simulator is 
> to be place in.    The simulator is 10’0” high which will leave 2in clearance 
> between it and the ceiling.    The simulator will be situated so that there 
> will be 18” of clearance between itself and the 3 walls surrounding it.    
> The footprint of the simulator is 9’6”x16’6”.
>
>   
>
> 1)            Do I need    sprinklers in the simulator?
>
>   
>
> 2)            Since there is only two inches of space above the simulator do 
> I even need sprinklers in the ceiling above it?   
>
>   
>
>   
>
>   
>
> My thought was to provide ceiling protection for the pockets created on the 
> sides of the simulator and put sprinklers in the simulator itself.
>
>   
>
>   
>
>   
>
> Thanks,
>
>   
>
>   
>
>   
>
> Dewayne Martinez
>
>   
>
> Fire Protection Design Manager
>
>   
>
>   
>
>   
>
> TOTAL   Mechanical
>
>   
>
> Building   Integrity
>    W234 N2830 Paul Rd.
>  Pewaukee, WI    53072
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
> Ph:    262-522-7110
>
>   
>
>  Cell: 414-406-5208
>
>   
>
>   http://www.total-mechanical.com/
>
>   
>
>   
>
>   
>
>                     
>
>   
>
>     
>
>   
>
>   
>
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to