From: Thomas Reinhardt
Sent: Thursday, June 08, 2017 10:53 AM
To: '[email protected]'
Subject: Do they need sprinklers?

I have a place of religious worship(A3) not sprinklered. They want to open up 
an elementary school in the basement(below grade) which has currently multiple 
rooms. Ages of children five through thirteen. We use IFC and IBC 2012 edition. 
The occupancy for the school I believe would be Education, thus Accessory to 
place of worship as defined in the IFC. If occupant load is less than 100 it 
shall be classified as an A3. Chapter 9 section 903.2.1.3(Fire Protection) 
relates that the fire area is located on a floor other than level of exit 
discharge it must be sprinklered. Also group E (903.2.3) say the same. I 
contend that they must not only sprinkler the basement, but also the entire 
building as interpreted in NFPA(2010 edition) chapter 4 section 4.1. Sorry so 
long . Any comments would be appreciated.
Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
[email protected]<mailto:[email protected]>