That would be a combustible concealed space everywhere around here.

On Fri, Jul 7, 2017 at 8:03 AM, Anthony Carrizosa <
anth...@archerconstruction.com> wrote:

> Looking at NFPA 13, see section 8.15.1.5
>
> *8.15.1.5 Localized Protection of Exposed Combustible Construction or
> Exposed Combustibles. When otherwise noncombustible or limited-combustible
> concealed spaces that would not require sprinkler protection have localized
> exposed combustible construction, or contain localized areas of exposed
> combustibles, the combustibles shall be permitted to be protected as
> follows:(1) If the exposed combustibles are in the vertical partitions or
> walls around all or a portion of the enclosure, a single row of sprinklers
> spaced not over 12 ft (3.7 m) apart nor more than 6 ft (1.8 m) from the
> inside of the partition shall be permitted to protect the surface. The
> first and last sprinklers in such a row shall not be over 5 ft (1.5 m) from
> the ends of the partitions.(2) If the exposed combustibles are in the
> horizontal plane, the area of the combustibles shall be permitted to be
> protected with sprinklers on a light hazard spacing. Additional sprinklers
> shall be installed no more than 6 ft(1.8 m) outside the outline of the area
> and not more than12 ft (3.7 m) on center along the outline. When the
> outline returns to a wall or other obstruction, the last sprinkler shall
> not be more than 6 ft (1.8 m) from the wall or obstruction.*
>
>
>
> Hope this helps.
>
> *Anthony Carrizosa *
>
> *Fire Protection Division *
>
> *OFFICE: 253-872-7222 <253-872-7222> *
>
> *Cell:         **206-679-5283 <(206)%20679-5283>*
>
> *[image: cid:703393518@19082013-11F7]*
>
>
>
>
>
> *From:* Brian Harris [mailto:bhar...@bvssystemsinc.com]
> *Sent:* Friday, July 07, 2017 7:29 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Looking For Opinions
>
>
>
> Working on a wood building per NFPA-13. Contract drawings show drywall
> above ceiling running to deck, GC stopped drywall 8” above ceiling leaving
> exposed wood & insulation. Any way this area won’t need sprinklers? See
> link for pictures.
>
>
>
> https://www.dropbox.com/sh/7mwoppgmu5aq27e/AADOdqgkge40MHXeUsex9RHSa?dl=0
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> Design Manager
>
> bvssystemsinc.com
>
> Phone: 704.896.9989 <(704)%20896-9989>
>
> Fax: 704.896.1935 <(704)%20896-1935>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to