Funny you should ask!

Original installation was designed for conventional Rack storage of Class I-IV 
Commodities using SR 17/32" heads without

in-rack sprinklers.


The owner changed it to a Mobile Shelving System with only a space for the 
retrieval vehicle to drive between the

aisles which move so they can get to the file being retrieved. There are a 
total of 5 of these movable shelves so at

all times there is only one space that is open. Oh btw there are solid shelves 
in each of the movable shelves.


I think it was one of your fellow U of M grads but I'm not sure.....LOL


Mike




________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Roland Huggins <[email protected]>
Sent: Wednesday, July 19, 2017 11:38 AM
To: [email protected]
Subject: Re: ESFR's in Buildings with Concrete Double Tee Construction

Houston - we have a problem.  What criteria allowed placing ESFR sprinklers 
below the tees?  That allowance is in 8.6 thus applies only to spray sprinklers

Roland



Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org<http://www.firesprinkler.org/>


Fire Sprinklers Saves Lives




On Jul 19, 2017, at 7:33 AM, Mike Hairfield 
<[email protected]<mailto:[email protected]>> wrote:

Thanks Roland,

This situation has 24" deep double tees that are 4'-0" o.c. and the heads are 
spaced 8"-0" o.c.
with the lines installed below the bottom of the tees.

Somebody has a major problem if ever catches on fire.

Mike


________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Roland Huggins 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, July 19, 2017 10:17 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: ESFR's in Buildings with Concrete Double Tee Construction

The noncombustible construction is not an issue for ant of the ESFR’s.  It’s 
the solid channel greater than 12 inches deep that stop things.  Well actually 
it’s the must be installed in every channel requirement while maintaining the 
min 8 ft separation that kills it. (See section 8.4.6.3.1 & .2)

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




On Jul 19, 2017, at 6:47 AM, Mike Hairfield 
<[email protected]<mailto:[email protected]>> wrote:

Have I missed something!

Have K25.2 ESFR sprinklers been approved to protect buildings that are 
constructed with
a concrete double tees roof construction?

Thanks,

Mike Hairfield
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to