I agree that sprinklers below would be required.  As the fire sprinkler 
installation designer, I would be pushing for uprights on exposed piping below 
the wood ceiling.  I'm sure that is not the look they are going for, so I 
imagine it would be an uphill climb to get that approved.  I might try to 
convince them to space the slats 1'-6" or greater apart.  Then your 72% 
improves and you meet the "least dimension of opening rule."

Micah Davis, SET
www.dynamicfiredesigns.com


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: Tuesday, July 25, 2017 1:04 PM
To: [email protected]
Subject: Tartan Wood Ceiling

Question. The general has informed me that they want to put in a tartan wood 
ceiling at  various spots. The wood slats are 1'-6" deep and just 2" wide, but 
are spaced at various dimensions- some as wide as 3' apart-some as close as 7". 
The with uprights will be at least 2'-4" above the top of wood. If they have to 
protect underneath would mean dropping pendants between wood slats with the 
deflector 1"-6" below the bottom of the wood. This could be quite an 
installation problem. NFPA 13 section 8.15.14 relates as long as ceiling is 70% 
open and the depth of the material does not exceed the least dimension of the 
opening, below protection is not required. Well the open ceiling is 72% open. 
Unfortunately the depth of the material does exceed the least dimension of the 
opening. I believe that below protection is required. Thus meeting the code. 
Sorry so long any input would be greatly appreciated. Thanks
Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342