Did you arrive at 72% using the nominal dimension of the wood or actual 
dimension.

Best 

Bruce Verhei 


> On Jul 26, 2017, at 08:19, Roland Huggins <[email protected]> wrote:
> 
> The conservative answer is put sprinklers beneath the ceiling fixtures BUT:
> 
> I wouldn’t apply the gridded ceiling criteria here since that is a sub 
> ceiling that covers the entire plane (beneath the sprinklers) and consists of 
> rather small opening.
> 
> If anything, I’d look at it like a cluster of obstructions to determine 
> whether to combine them in defining the overall width.  This is only found in 
> the ESFR section (which is much more conservative than the CMDA approach 
> required not just for the performance issue but the fact that the fire 
> challenge is much greater than a LH or OH scenario)
> 
> Keep in mind that the primary goal is to control the upper temperature so as 
> to avoid flashover.  We are talking LH or OH - right?  Granted the water 
> pattern to the floor is going to be whacked (well for the areas with a 7” 
> spacing) but will the ceiling features interfere with controlling flashover?  
> Another question is, will the sprinkler beneath the features even activate 
> (except when the fire is directly beneath it)?
> 
> I don’t think the simple conservative approach is accomplishing anything 
> except providing a warm fuzzy but it does allow the job to move forward.  So 
> until NFPA 13 addresses it (NEXT CYCLE), discuss it with the AHJ BEFORE 
> submitting your plans
> 
> Tom, since we don’t want you talking to yourself,  feel free to call me.
> 
> Roland
> 
> 
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.    
> Dallas, TX
> http://www.firesprinkler.org
> 
> Fire Sprinklers Saves Lives
> 
> 
> 
> 
>> On Jul 25, 2017, at 11:04 AM, Thomas Reinhardt <[email protected]> 
>> wrote:
>> 
>> Question. The general has informed me that they want to put in a tartan wood 
>> ceiling at  various spots. The wood slats are 1’-6” deep and just 2” wide, 
>> but are spaced at various dimensions- some as wide as 3’ apart-some as close 
>> as 7”. The with uprights will be at least 2’-4” above the top of wood. If 
>> they have to protect underneath would mean dropping pendants between wood 
>> slats with the deflector 1”-6” below the bottom of the wood. This could be 
>> quite an installation problem. NFPA 13 section 8.15.14 relates as long as 
>> ceiling is 70% open and the depth of the material does not exceed the least 
>> dimension of the opening, below protection is not required. Well the open 
>> ceiling is 72% open. Unfortunately the depth of the material does exceed the 
>> least dimension of the opening. I believe that below protection is required. 
>> Thus meeting the code. Sorry so long any input would be greatly appreciated. 
>> Thanks
>> Tom Reinhardt
>> Fire Inspector/Plan Reviewer
>> Skokie Fire Department
>> 7424 Niles Center Road
>> Skokie, IL 60077
>> Office: 847-982-5342
>> [email protected]
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to