Thanks Scot. The foam systems I have dealt with In the past have been in large 
open areas (hangers). Still waiting on occupancy details
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On Sep 26, 2017 at 9:37 AM,  <å... .... (mailto:[email protected])>  
> wrote:
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  Todd:
>   
>   
>   
>  Closed heads operate individually.    
>   
>   
>   
>   
>   
>  Assume the hazard is liquid fuelled fire:
>   
>   
>   
>             1. if closed room, where is oxygen going to come from to support 
> sustained pool fire over entire area, and
>   
>   
>   
>             2.    if such a fire were supported with oxygen, I think the room 
> occupants have hotter issues than avoiding the foam.
>   
>   
>   
>             3. to fill the floor with a spill (but not a pool fire in depth) 
> will require about 15 gallons.      
>   
>              Would not most room occupants notice something wrong before 15 
> gallons spilled on the floor.
>   
>   
>   
>             4. short of a reasonable worse-case scenario, which is fire 
> across entire room area burning liquid, most other   
>   
>                 fires will be less big, and / or slower growing.      
>   
>   
>   
>             5.    If the liquid fuel fire occupied only half the floor area, 
> the time for the leak to occur is shorter.    Still, will
>   
>              not most occupants realize what is happening while 7 gallons of 
> fuel are spilling onto the floor, and have
>   
>              time to make a hasty exit before ignition?
>   
>   
>   
>             6.    if the liquid fuel spill is 7 gallon, and it is 
> instantaneous across half the surface of this 300 sq. ft. room, then
>   
>             my advice is the hazardous substance was not well confined in a   
>  double wall or dual barrier container.
>   
>   
>   
>             7    If the room is an anechoic chamber and the combustible is 
> foam, then there should be signs in the room and
>   
>             on the entry door to RUN in case of fire.
>   
>   
>   
>             8.    Is it a Ronald McDonald playroom filled with plastic balls 
> intended for children?
>   
>   
>   
>  I don't see, however, many scenarios, where the fire will open enough 
> sprinklers releasing enough foam quick enough
>   
>  for someone to exit a 300 sq. ft. room before the foam is 6ft high.
>   
>   
>   
>          Maybe you want to sign the room for life safety hazard.
>   
>          Maybe you want a visual signal to accompany release (rotating red 
> strobe)
>   
>          Maybe a better description of the room (is it an accessible (ADA) 
> space),   
>   
>                         the occupancy,   
>   
>                         the intended users,   
>   
>                         the travel distance
>   
>                         the foam (is it Hi-X, CAF or Lo-X),   
>   
>         
>   
>  Scot Deal
>   
>  Excelsior Risk  &  Fire   
>   
>  gms:    + 420 608 318 498
>   
>
>   
> On Tue, Sep 26, 2017 at 2:26 PM,  <[email protected] 
> (mailto:[email protected])>  wrote:
>   
> >   
> >   
> >   
> >
> >  Since I couldn't find the Foam Forum, I figured I would ask this here. I 
> > have been asked to design a modification to an existing foam system inside 
> > a building. I am still trying to get details on occupancy, design, etc. 
> > There is no one in the room on a regular basis, but there is occasionally. 
> > My concern (at this point) is that they are asking for 7 sprinklers 
> > (closed) in a 300 sqft room. Are there any life safety concerns with this? 
> > I wouldn't want to see someone get trapped in a room filling up with foam.  
> >  
> >   
> >   
> >   
> >  Todd G Williams, PE  
> > Fire Protection Design/Consulting
> >   
> > Stonington, CT
> >   
> > 860-535-2080 (tel:860-535-2080)  (ofc)
> >   
> > 860-553-3553 (tel:860-553-3553)  (fax)
> >   
> > 860-608-4559 (tel:860-608-4559)  (cell)
> >   
> >   
> >   
> >   
> >
> >   
> >   
> >   
> >  _______________________________________________
> >  Sprinklerforum mailing list
> >   [email protected] 
> > (mailto:[email protected])
> >   
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >   
>        _______________________________________________ Sprinklerforum mailing 
> list [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>            
  

  
 