Kyle,

No, the 4 floors combined are over 52,000. We will make sure that we meet
the water delivery requirements.

Thanks for the input,
Ben


Benjamin Young

On Mon, Oct 2, 2017 at 11:34 AM, Kyle.Montgomery <[email protected]>
wrote:

> Are the 4 floors combined less than 52,000 sq. ft.? Or are they just
> individually less than 52,000 sq. ft.? Are you pretty confident you can
> meet the water delivery times with all four floors on one valve?
>
>
>
> *Kyle Montgomery*
>
>  [image: cid:[email protected]]
>
> *Aero Automatic Sprinkler Co.*
>
> *21605 N. Central Ave.*
>
> *Phoenix, AZ 85024*
>
> *Direct: 623.580.7820 <(623)%20580-7820>*
>
> *Cell: 602.763.4736 <(602)%20763-4736>*
>
> [email protected]
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Ben Young
> *Sent:* Monday, October 02, 2017 7:44 AM
> *To:* [email protected]
> *Subject:* [EXTERNAL] dry systems in parking garages exception
>
>
>
> NFPA 13, 2016 edition has what appears to be a new section, 8.2.4.4, that
> allows one to disregard the requirements of 8.2.4 (control valves for each
> floor in multi-story building) when doing dry pipe systems in parking
> garages.
>
>
>
> The reason I say appears to be new, is because they relocated the control
> valve requirements to 8.2.4 in 2016 from 8.16.1.5 in 2013, but the language
> of 8.2.4.4 wasn't in that section in 2013.
>
>
>
> I mean, it makes sense since you can't have a FCVA on a dry pipe system,
> but we're doing a 4-story parking garage under the 2013 edition and I'm
> trying to make sure we're not going be slammed by the AHJ to provide 4 dry
> valves!
>
>
>
> Can anyone let me know if the verbiage in 8.2.4.4 exists in editions of
> NFPA 13 prior to the 2016 edition?
>
>
>
> Thanks,
>
>
> Ben Young
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to