DEKS Dektite Original #3 Silicone roofing boot model DF203RE with 8" base o.d. 
When the plenum is a sealed space, use the boot on the pipe where it enters the 
plenum and also at the sprinkler.

On Wed, Oct 18, 2017 at 6:50 AM, AKS-Gmail-IMAP 
<[email protected]<mailto:[email protected]>> wrote:
For the situation where the ceiling is a solid composite panel below a 
pressurized plenum there is a particular brand of flexible roof boot designed 
to handle pipe penetrations at a roof that will work. I do not have the name 
off hand. In my area it comes out of Chicago. Imagine a rubber device that is 
not unlike the flexible boot for a car’s stick shifter. Its end that attaches 
to the roof is large enough to comfortably fit over the sprinkler. The other 
end that you cut to size will fit a 1” pipe. You will have to call to make sure 
the dimensions work since none of the manufactures for this type of product 
post the dimensions and most are not large enough to fit over the sprinkler. 
The guy I called actually had one in his hands, so he could measure its 
business end while we talked. The product has a ring for fastening to a metal 
deck. Apply silicone seal there and also where the boot grips the 1” pipe. The 
boot will isolate the sprinkler from the pressurized plenum.

Allan Seidel
St. Louis, MO


On Oct 17, 2017, at 2:16 PM, Larrimer, Peter A 
<[email protected]<mailto:[email protected]>> wrote:

Can anyone please assist with a recommendation for a “clean room” sprinkler 
where the clean rooms are designed to be negative pressure (for compounding 
dangerous drugs).

The concealed sprinkler cut sheets that I’ve looked at online generally say 
that the concealed heads cannot be used in negative pressure rooms (positive 
pressure plenums) and this is the type of room design that we require.  The 
FlexHead cleanroom ceiling sprinkler connection doesn’t appear to be easy to 
clean after installation.

What type of quick response sprinkler could be used in a negative pressure room 
that is readily and easily cleanable?  Users wanted to used concealed 
sprinklers as they thought that the concealed sprinklers would be easy to wipe 
down when necessary, but we don’t want to violate the installation instructions 
on the cut sheets that state that the concealed sprinklers can’t be used with 
positive pressure plenums (negative pressure rooms).

Thanks in advance.