If you have a LH or OH criteria where the concealed heads can be used, one 
method that was approved by one of the big insurers for a similar installation 
used the TYCO DSB-2 dry sprinkler boot on the sprinkler drop.  The boot was 
placed over the drop and sealed against the upper side of the celling panel.  
The concealed sprinkler used the gasket option on the room side of the 
sprinkler.

This method according to the underwriter had been proven to stop any 
infiltration into the occupied space from the ceiling cavity.

But if you have an EH occupancy, then that’s another story.

I would highly recommend contacting the owner’s Risk Consultant or Insurance 
Underwriter or EOR for input or approval on any method proposed.

Since this could be a “H” occupancy I do certainly hope there is a qualified 
engineer involved in the project.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, October 17, 2017 3:16 PM
To: [email protected]
Subject: Clean Room Sprinkler Options [EXTERNAL]

Can anyone please assist with a recommendation for a “clean room” sprinkler 
where the clean rooms are designed to be negative pressure (for compounding 
dangerous drugs).

The concealed sprinkler cut sheets that I’ve looked at online generally say 
that the concealed heads cannot be used in negative pressure rooms (positive 
pressure plenums) and this is the type of room design that we require.  The 
FlexHead cleanroom ceiling sprinkler connection doesn’t appear to be easy to 
clean after installation.

What type of quick response sprinkler could be used in a negative pressure room 
that is readily and easily cleanable?  Users wanted to used concealed 
sprinklers as they thought that the concealed sprinklers would be easy to wipe 
down when necessary, but we don’t want to violate the installation instructions 
on the cut sheets that state that the concealed sprinklers can’t be used with 
positive pressure plenums (negative pressure rooms).

Thanks in advance.

Pete Larrimer
VA