Our company will typical groove / weld down to 1-1/4", and thread 1". The
decision on whether to groove or thread typical depend on the number of
outlets. Its quicker for our installer to install one pipe verses many
sticks on a single run. 

 

On our jobs we don't typical see a limitation on the grooved size. We do see
it on the pipe schedule. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Prahl, Craig/GVL
Sent: Monday, November 20, 2017 11:54 AM
To: [email protected]
Subject: 1" grooved pipe and couplings and 2" and below grooved pipe 

 

I'm wondering what the consensus is amongst the group here on a couple
issues as I look towards making some updates to our project specifications.


 

#1,  the use of 1" grooved pipe and fittings versus threaded.  This would be
using Sch. 40 pipe.  I saw a presentation which if I were still a contractor
would definitely make me take a good hard look at utilizing this technology.
Do you use this or are contemplating using it?  

 

#2, the use of grooved pipe and fitting on pipe below 2" in diameter.  Seems
like the typical spec lists grooved for pipe above 2" but threaded below 2".
Why?  Why not grooved pipe below 2"?  

 

I would appreciate some thoughts and incite from those in the field.

 

Thanks,


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to