Yeah, it’s called the “God Clause” out here …

That’s not in the sprinkler standard and it’s not required in our 
(California-amended) building code either.  What is required is that the 
sprinkler systems in the tenant spaces be separate from the ones in common 
spaces and in anchor stores for open and covered malls as they are defined in 
the code.  But the tenant spaces are NOT required to be individually zoned or 
sectionally controlled.

HOWEVER … over the years I’ve worked on several mall projects where this was a 
thing.  One such project was to build a huge new wing on an existing mall.   
Four new systems – East and West/First and Second Floors.  Scope for the tenant 
shells was to run an 8” main down the line with outlets that each had a 
supervised butterfly valve, aux drain and a flow switch.  Sparky roughed a 
supervisory circuit to pick up the valve and flow switch.   But this was a 
giant mall that had conservative requirements for annunciation of each suite by 
floor and area.

So if it’s coming from the fire official, ask them where it’s published and to 
cite a section …

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Vince Sabolik
Sent: Tuesday, November 28, 2017 3:13 PM
To: [email protected]
Subject: Looking for specific sprinkler code on tenant spaces

Help!

We have an existing, sprinklered building - everything up to snuff.
It's being converted to tenant spaces

Is there specific code somewhere that allows an AHJ to require that each tenant 
space be given
it's own shutoff, flow switch and alarm?

thanks, Vince
[cid:[email protected]]

Vince Sabolik
West Tech Fire Protection, Inc.
11351 Pearl Road   /   Strongsville, Ohio   44136
Phone 440 238-4800    Fax  440 238-4876   Cell 440 724-7601