I mean, after all, if we can't figure 'half a pattern', how do sidewalls work?
I'm out, because... i, I mean Roland and that face, I mean...
Oh nevermind - - brad..

Quoting [email protected]:

Sorry John, wrong side of history on this one.
Brad.

Quoting John Paulsen <[email protected]>:

I've been watching this thread all afternoon and what I perceived to be a straight forward question has been complicated beyond anything I would have thought possible considering the original question. For me the bottom line here is that if you submit this layout and hydraulic calculations as anything other than the 14' dimension on the sloped ceiling, you are going to have to defend it to the AHJ. Any plan reviewer worth his salt is going to conclude that the vertical portion of the saw-tooth creates an obstruction to the spray pattern. That will demand the 7' distance be considered half the distance the head has to throw to obtain the correct spacing and design density. If this is OH as previously stated, in my mind, you are limited to 9' head spacing along the line.

However,

If you can get the AHJ and engineer to approve moving the sprinklers to the middle of the slope and keep the deflector above 12" from the highest point of the ceiling and in conformance with Table 8.6.5.1.2 distances from the obstruction, well then you might have a shot at the 15' head spacing along the line.

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of Michael Hill
Sent: Thursday, November 30, 2017 4:26 PM
To: [email protected]
Subject: RE: Saw-Tooth Ceilings

So you are saying that this is a series of 15 sloped ceilings one after the other, not a single obstructed saw tooth ceiling.

I am not trying to be argumentative. I am trying to convince myself that what I am being told to do is correct.

Mike Hill


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected]
Sent: Thursday, November 30, 2017 4:02 PM
To: [email protected]
Subject: Re: Saw-Tooth Ceilings

23.4.4.6 Deisign Densities
23.4.4.6.2, and for backup-
23.4.4.6.5.
You don't have walls Michael, you have a sloped ceiling.
The down-slope 'half' of the pattern is obstructed, be it sawtooth or not :).
Brad.

Quoting Michael Hill <[email protected]>:

That section explains what to do once the maximum area of protection
is determined. I am still not convinced.
I agree that plenty of water is going to get to the fire, if needed.
More so as this is a UFC project, HC-2 occupancy, dry system,
0.20/3500.

Suppose there were walls that extended down to the floor at each end
of the ceiling that created a compartment (which is how I am viewing
this situation). In this case the compartment would be 240' x 8'.
8.5.2 tells me to take the distance from the wall, double it and
multiply by the distance between sprinklers in the other direction.
No mention of if the area is broken down into smaller compartments.

Does anyone know of a section in NFPA-13 that allows me to ignore the
obstruction when determining area of protection per sprinkler.

This is how I look at things when I do not agree with them. I figure I
am sitting on a witness stand somewhere (after the fire the destroyed
the building) and some insurance company's' lawyer is saying "point to
where it says you can do that".

Mike Hill

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, November 30, 2017 2:34 PM
To: [email protected]
Subject: Re: Saw-Tooth Ceilings

I'm with Ron.
See NFPA 13-2016
23.4.4.6.2.
Brad.

Quoting Ron Greenman <[email protected]>:

I'll agree the sprinkler knows nothing, but that is irrelevant. We
are working with a mathematical model that will, if all the rules are
followed, give us a reasonable degree of confidence that it will
perform to the design intended, which is, in this case, to keep a
fire contained within the most demanding design area (or any other
similar, but less demanding
area) for a specified duration. So for OH I can space my sprinklers
along the ceiling at a MAXIMUM of 15 ft apart, in any direction
perpendicular to the walls, which is a maximum square footage per
sprinkler of 225 square feet, and a MINIMUM of six feet between them
for a total square footage of 36. So given Mike's layout, he is well
within the parameters of this rule.
Now though we run into another rule which states we cannot EXCEED 130
square feet of floor area per sprinkler in OH so if we run our
sprinklers at 15' apart on the line we can have a MAXIMUM distance
between lines a fraction over 8.5 feet. Since the sawtooth creates a
"compartment," so to speak, because of the obstructive nature of the
"wall" the "compartment"
distances are 8x15 per sprinkler so he is well within the spacing
rules regarding "throw," and since his horizontal space coverage area
at the floor is less than 130 sqft per sprinkler he is within the
area limitation for OH. His density will be a minimum of 0.15
gallons/min/sqft and presuming he has enough pressure to push that
quantity of water through the system to the 13 (before adjustments to
the design area, if any) design sprinklers the system will p[erform
as desired. Back to the ignorant sprinkler. Will it adjust to the
1.0'x7.5'x7.0'x7.5' layout and deliver exactly 0.15 gpm to each
square foot per minute? Of course not. What will happen though is the
system will supply enough water to up to 13 sprinklers anywhere in
the system to meet the design parameter (containment of the fire to
no more than 1500sqft). We can feel confident about this since
sprinkler systems have been doing so for over a hundred years both in
pipe schedule and hydraulically designed configurations. In every
system, there is a prize and that is containment or suppression of a
fire. There are several design methods to obtain the prize and 13 is
merely a prescriptive set of rules to get us there. As long as we
follow the rules we'll be alright. If we want to play mathematician
or fluid dynamicist then we'll cease to be layout technicians and
we'll get distracted and our eyes will stray from the prize.

On Thu, Nov 30, 2017 at 9:33 AM, Nick Maneen <[email protected]> wrote:

You are correct.  The sprinkler does not know it needs to throw
water in mainly one direction.  It will be 15x14



*Nick Maneen, SET *

*c* 704.791.7789 <(704)%20791-7789>



*From:* Sprinklerforum [mailto:[email protected].
org] *On Behalf Of *Michael Hill
*Sent:* Thursday, November 30, 2017 12:30 PM
*To:* [email protected]
*Subject:* RE: Saw-Tooth Ceilings



Yes, the actual floor area is about 120ft² per sprinkler. Each
sprinkler has to spray 7’-0” towards the next line. The next
sprinkler is within 1’-0” of the vertical portion of the ceiling
(which I am considering an
obstruction) and will not spray any further in that direction. The
water will hit the obstruction and fall straight down. I know the
sprinklers can cover that 7’-0” spray, but I need to make sure it
does so at the correct density. So for hydraulic purposes is the
spacing considered 120ft² or is it 210ft².



My take is that the sprinkler is 7’-0” form a wall or obstruction,
as the sprinkler has to spray 7’-0” to cover to the low portion of
the saw-toothed ceiling. L=14  and S=15. So hydraulically that
sprinkler has to cover 210ft². I would like to say it is covering
120ft² but I need to see where in NFPA-13 that it says I can do so.





Mike Hill



*From:* Sprinklerforum [mailto:[email protected].
org <[email protected]>] *On Behalf Of
*Ron Greenman
*Sent:* Thursday, November 30, 2017 12:09 PM
*To:* [email protected]
*Subject:* Re: Saw-Tooth Ceilings



If I'm understanding your description and question properly you are
covering about 116-117 sqft of floor area if one considers the 1'8"
rise at the tip of the tooth an obstruction, which I would, and your
"throw distance" along the slope is at 0-360 degrees=7.5'/90
degrees=7.0'/180
degrees=7.5 degrees/270 degrees=1.0'. That puts you within coverage
rules for OH, and throw range rules for SS sprinklers.



On Thu, Nov 30, 2017 at 8:33 AM, Michael Hill <[email protected]> wrote:

I am working on a firing range that is going to have a saw-tooth
type ceiling installed. I have a question about determining maximum
protection area per sprinkler.



The vertical portion is 1’-8” tall with the distance from the high
point to the low point being 8’-0”, measured along the slope.
Sprinklers need to be spaced close to the vertical portion of the
ceiling, to protect them from stray projectiles. The sprinkler will
end up being about 7’-0” from the low point of the ceiling, measured
along the slope. The sprinklers are about 8’-0” apart, but with a
1’-8” vertical portion of the ceiling between them. Sprinklers are
spaced 15’-0” apart along the branchline. See attached sketch (if it
came through).



Would the spacing be 15’ x 8’ or would it be 15’ x 14’?



I feel it should be 15’ x 14’ as any individual sprinkler needs to
cover 7’-0” in one direction, measured along the slope. I feel the
vertical portion of the ceiling is an obstruction and can almost
been interpreted as a wall that extends to the floor. I also thought
I needed to increase my design area for sloped ceiling for this
situation, but have since been shown the commentary in the handbook
that explains why it is not required for saw-toothed ceilings.
Maybe I am wrong about the spacing as well.









Mike Hill




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
org





--

Ron Greenman


[email protected]

253.576.9700 <(253)%20576-9700>



The Universe is monstrously indifferent to the presence of man.
-Werner Herzog, screenwriter, film director, author, actor and opera
director (1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
org




--
Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man.
-Werner Herzog, screenwriter, film director, author, actor and opera
director (1942-)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to