With all this talk about spacing, I think maybe the text within NFPA 13 has 
been forgotten. Here's what the standard says on the subject of saw-tooth 
ceilings:

8.6.4.1.3.2*   Under saw-toothed roofs, sprinklers at the highest elevation 
shall not exceed a distance of 36 in. (900 mm) measured down the slope from the 
peak.

A.8.6.4.1.3.2   Saw-toothed roofs have regularly spaced monitors of saw tooth 
shape, with the nearly vertical side glazed and usually arranged for venting. 
Sprinkler placement is limited to a maximum of 3 ft (900 mm) down the slope 
from the peak because of the effect of venting on sprinkler sensitivity.

My advice would be to move the sprinkler to a point 3 ft from the peak. That 
way it will be about 5 ft from the low edge instead of 7 ft, which should 
alleviate the spray/obstruction/spacing problem somewhat.

This is my opinion only and is not intended to represent the NFPA 13 Technical 
Committee, nor serve as an interpretation of the standard.

Larry Keeping


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: November-30-17 6:39 PM
To: [email protected]
Subject: Re: Saw-Tooth Ceilings

I mean, after all, if we can't figure 'half a pattern', how do sidewalls work?
I'm out, because... i, I mean Roland and that face, I mean...
Oh nevermind - - brad..

Quoting [email protected]:

> Sorry John, wrong side of history on this one.
> Brad.
>
> Quoting John Paulsen <[email protected]>:
>
>> I've been watching this thread all afternoon and what I perceived  
>> to be a straight forward question has been complicated beyond  
>> anything I would have thought possible considering the original  
>> question. For me the bottom line here is that if you submit this  
>> layout and hydraulic calculations as anything other than the 14'  
>> dimension on the sloped ceiling, you are going to have to defend it  
>> to the AHJ. Any plan reviewer worth his salt is going to conclude  
>> that the vertical portion of the saw-tooth creates an obstruction  
>> to the spray pattern. That will demand the 7' distance be  
>> considered half the distance the head has to throw to obtain the  
>> correct spacing and design density. If this is OH as previously  
>> stated, in my mind, you are limited to 9' head spacing along the  
>> line.
>>
>> However,
>>
>> If you can get the AHJ and engineer to approve moving the  
>> sprinklers to the middle of the slope and keep the deflector above  
>> 12" from the highest point of the ceiling and in conformance with  
>> Table 8.6.5.1.2 distances from the obstruction, well then you might  
>> have a shot at the 15' head spacing along the line.
>>
>> John Paulsen – SET
>> Crown Fire System Design
>> 6282 Seeds Rd.
>> Grove City, OH 43123
>> P – 614-782-2438
>> F – 614-782-2374
>> C – 614-348-8206
>>
>>
>>
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum  
>> [mailto:[email protected]] On Behalf  
>> Of Michael Hill
>> Sent: Thursday, November 30, 2017 4:26 PM
>> To: [email protected]
>> Subject: RE: Saw-Tooth Ceilings
>>
>> So you are saying that this is a series of 15 sloped ceilings one  
>> after the other, not a single obstructed saw tooth ceiling.
>>
>> I am not trying to be argumentative. I am trying to convince myself  
>> that what I am being told to do is correct.
>>
>> Mike Hill
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum  
>> [mailto:[email protected]] On Behalf  
>> Of [email protected]
>> Sent: Thursday, November 30, 2017 4:02 PM
>> To: [email protected]
>> Subject: Re: Saw-Tooth Ceilings
>>
>> 23.4.4.6 Deisign Densities
>> 23.4.4.6.2, and for backup-
>> 23.4.4.6.5.
>> You don't have walls Michael, you have a sloped ceiling.
>> The down-slope 'half' of the pattern is obstructed, be it sawtooth  
>> or not :).
>> Brad.
>>
>> Quoting Michael Hill <[email protected]>:
>>
>>> That section explains what to do once the maximum area of protection
>>> is determined. I am still not convinced.
>>> I agree that plenty of water is going to get to the fire, if needed.
>>> More so as this is a UFC project, HC-2 occupancy, dry system,
>>> 0.20/3500.
>>>
>>> Suppose there were walls that extended down to the floor at each end
>>> of the ceiling that created a compartment (which is how I am viewing
>>> this situation). In this case the compartment would be 240' x 8'.
>>> 8.5.2 tells me to take the distance from the wall, double it and
>>> multiply by the distance between sprinklers in the other direction.
>>> No mention of if the area is broken down into smaller compartments.
>>>
>>> Does anyone know of a section in NFPA-13 that allows me to ignore the
>>> obstruction when determining area of protection per sprinkler.
>>>
>>> This is how I look at things when I do not agree with them. I figure I
>>> am sitting on a witness stand somewhere (after the fire the destroyed
>>> the building) and some insurance company's' lawyer is saying "point to
>>> where it says you can do that".
>>>
>>> Mike Hill
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of
>>> [email protected]
>>> Sent: Thursday, November 30, 2017 2:34 PM
>>> To: [email protected]
>>> Subject: Re: Saw-Tooth Ceilings
>>>
>>> I'm with Ron.
>>> See NFPA 13-2016
>>> 23.4.4.6.2.
>>> Brad.
>>>
>>> Quoting Ron Greenman <[email protected]>:
>>>
>>>> I'll agree the sprinkler knows nothing, but that is irrelevant. We
>>>> are working with a mathematical model that will, if all the rules are
>>>> followed, give us a reasonable degree of confidence that it will
>>>> perform to the design intended, which is, in this case, to keep a
>>>> fire contained within the most demanding design area (or any other
>>>> similar, but less demanding
>>>> area) for a specified duration. So for OH I can space my sprinklers
>>>> along the ceiling at a MAXIMUM of 15 ft apart, in any direction
>>>> perpendicular to the walls, which is a maximum square footage per
>>>> sprinkler of 225 square feet, and a MINIMUM of six feet between them
>>>> for a total square footage of 36. So given Mike's layout, he is well
>>>> within the parameters of this rule.
>>>> Now though we run into another rule which states we cannot EXCEED 130
>>>> square feet of floor area per sprinkler in OH so if we run our
>>>> sprinklers at 15' apart on the line we can have a MAXIMUM distance
>>>> between lines a fraction over 8.5 feet. Since the sawtooth creates a
>>>> "compartment," so to speak, because of the obstructive nature of the
>>>> "wall" the "compartment"
>>>> distances are 8x15 per sprinkler so he is well within the spacing
>>>> rules regarding "throw," and since his horizontal space coverage area
>>>> at the floor is less than 130 sqft per sprinkler he is within the
>>>> area limitation for OH. His density will be a minimum of 0.15
>>>> gallons/min/sqft and presuming he has enough pressure to push that
>>>> quantity of water through the system to the 13 (before adjustments to
>>>> the design area, if any) design sprinklers the system will p[erform
>>>> as desired. Back to the ignorant sprinkler. Will it adjust to the
>>>> 1.0'x7.5'x7.0'x7.5' layout and deliver exactly 0.15 gpm to each
>>>> square foot per minute? Of course not. What will happen though is the
>>>> system will supply enough water to up to 13 sprinklers anywhere in
>>>> the system to meet the design parameter (containment of the fire to
>>>> no more than 1500sqft). We can feel confident about this since
>>>> sprinkler systems have been doing so for over a hundred years both in
>>>> pipe schedule and hydraulically designed configurations. In every
>>>> system, there is a prize and that is containment or suppression of a
>>>> fire. There are several design methods to obtain the prize and 13 is
>>>> merely a prescriptive set of rules to get us there. As long as we
>>>> follow the rules we'll be alright. If we want to play mathematician
>>>> or fluid dynamicist then we'll cease to be layout technicians and
>>>> we'll get distracted and our eyes will stray from the prize.
>>>>
>>>> On Thu, Nov 30, 2017 at 9:33 AM, Nick Maneen <[email protected]> wrote:
>>>>
>>>>> You are correct.  The sprinkler does not know it needs to throw
>>>>> water in mainly one direction.  It will be 15x14
>>>>>
>>>>>
>>>>>
>>>>> *Nick Maneen, SET *
>>>>>
>>>>> *c* 704.791.7789 <(704)%20791-7789>
>>>>>
>>>>>
>>>>>
>>>>> *From:* Sprinklerforum  
>>>>> [mailto:[email protected].
>>>>> org] *On Behalf Of *Michael Hill
>>>>> *Sent:* Thursday, November 30, 2017 12:30 PM
>>>>> *To:* [email protected]
>>>>> *Subject:* RE: Saw-Tooth Ceilings
>>>>>
>>>>>
>>>>>
>>>>> Yes, the actual floor area is about 120ft² per sprinkler. Each
>>>>> sprinkler has to spray 7’-0” towards the next line. The next
>>>>> sprinkler is within 1’-0” of the vertical portion of the ceiling
>>>>> (which I am considering an
>>>>> obstruction) and will not spray any further in that direction. The
>>>>> water will hit the obstruction and fall straight down. I know the
>>>>> sprinklers can cover that 7’-0” spray, but I need to make sure it
>>>>> does so at the correct density. So for hydraulic purposes is the
>>>>> spacing considered 120ft² or is it 210ft².
>>>>>
>>>>>
>>>>>
>>>>> My take is that the sprinkler is 7’-0” form a wall or obstruction,
>>>>> as the sprinkler has to spray 7’-0” to cover to the low portion of
>>>>> the saw-toothed ceiling. L=14  and S=15. So hydraulically that
>>>>> sprinkler has to cover 210ft². I would like to say it is covering
>>>>> 120ft² but I need to see where in NFPA-13 that it says I can do so.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Mike Hill
>>>>>
>>>>>
>>>>>
>>>>> *From:* Sprinklerforum  
>>>>> [mailto:[email protected].
>>>>> org <[email protected]>] *On Behalf Of
>>>>> *Ron Greenman
>>>>> *Sent:* Thursday, November 30, 2017 12:09 PM
>>>>> *To:* [email protected]
>>>>> *Subject:* Re: Saw-Tooth Ceilings
>>>>>
>>>>>
>>>>>
>>>>> If I'm understanding your description and question properly you are
>>>>> covering about 116-117 sqft of floor area if one considers the 1'8"
>>>>> rise at the tip of the tooth an obstruction, which I would, and your
>>>>> "throw distance" along the slope is at 0-360 degrees=7.5'/90
>>>>> degrees=7.0'/180
>>>>> degrees=7.5 degrees/270 degrees=1.0'. That puts you within coverage
>>>>> rules for OH, and throw range rules for SS sprinklers.
>>>>>
>>>>>
>>>>>
>>>>> On Thu, Nov 30, 2017 at 8:33 AM, Michael Hill  
>>>>> <[email protected]> wrote:
>>>>>
>>>>> I am working on a firing range that is going to have a saw-tooth
>>>>> type ceiling installed. I have a question about determining maximum
>>>>> protection area per sprinkler.
>>>>>
>>>>>
>>>>>
>>>>> The vertical portion is 1’-8” tall with the distance from the high
>>>>> point to the low point being 8’-0”, measured along the slope.
>>>>> Sprinklers need to be spaced close to the vertical portion of the
>>>>> ceiling, to protect them from stray projectiles. The sprinkler will
>>>>> end up being about 7’-0” from the low point of the ceiling, measured
>>>>> along the slope. The sprinklers are about 8’-0” apart, but with a
>>>>> 1’-8” vertical portion of the ceiling between them. Sprinklers are
>>>>> spaced 15’-0” apart along the branchline. See attached sketch (if it
>>>>> came through).
>>>>>
>>>>>
>>>>>
>>>>> Would the spacing be 15’ x 8’ or would it be 15’ x 14’?
>>>>>
>>>>>
>>>>>
>>>>> I feel it should be 15’ x 14’ as any individual sprinkler needs to
>>>>> cover 7’-0” in one direction, measured along the slope. I feel the
>>>>> vertical portion of the ceiling is an obstruction and can almost
>>>>> been interpreted as a wall that extends to the floor. I also thought
>>>>> I needed to increase my design area for sloped ceiling for this
>>>>> situation, but have since been shown the commentary in the handbook
>>>>> that explains why it is not required for saw-toothed ceilings.
>>>>> Maybe I am wrong about the spacing as well.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Mike Hill
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>>>>> org
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> --
>>>>>
>>>>> Ron Greenman
>>>>>
>>>>>
>>>>> [email protected]
>>>>>
>>>>> 253.576.9700 <(253)%20576-9700>
>>>>>
>>>>>
>>>>>
>>>>> The Universe is monstrously indifferent to the presence of man.
>>>>> -Werner Herzog, screenwriter, film director, author, actor and opera
>>>>> director (1942-)
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>>>>> org
>>>>>
>>>>>
>>>>
>>>>
>>>> --
>>>> Ron Greenman
>>>>
>>>> [email protected]
>>>>
>>>> 253.576.9700
>>>>
>>>> The Universe is monstrously indifferent to the presence of man.
>>>> -Werner Herzog, screenwriter, film director, author, actor and opera
>>>> director (1942-)
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to