Based on what, specifically?


Steve


-------- Original message --------
From: tcfire <tcf...@bellsouth.net>
Date: 12/21/17 5:54 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion

Seems to make a great argument for nitrogen infusion.



Sent from my Sprint Samsung Galaxy S7.

-------- Original message --------
From: Steve Leyton <st...@protectiondesign.com>
Date: 12/20/17 8:51 PM (GMT-05:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion

The fact that the adjacent systems haven’t leaked is not surprising – we’re 
working on remediation of three large buildings right now where only one of the 
three systems in each has demonstrated corrosion outwardly through pinhole 
leaks.  When we scoped the systems, all of them showed aggressive corrosion 
related to MIC, but only one had advanced to the degree that the pipe was 
beginning to fail.   None of the nine systems we’re working with show ANY 
external signs of the advanced damage we found inside.

Someone else mentioned on this thread that resolving leaks in that one system 
was regularly introducing fresh oxygen and that’s true; it may explain why it’s 
more advanced than the others.

[Steve Signature (3)]

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Wednesday, December 20, 2017 3:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Corrosion

I’m relying on Lucas to correct any statement that are just wrong but - 
predicting corrosion is a lot like predicting a medical disease.  We know a lot 
of facts that affect the issue but there’s a SH factor that’s not yet 
quantifiable.  SH = Stuff Happens

After seven events, why haven’t they pursued active mitigation?

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




On Dec 20, 2017, at 2:37 PM, Mike Hairfield 
<fsl...@msn.com<mailto:fsl...@msn.com>> wrote:

Trying to explain to the owner why it's happened seven (7) times on the same 
system
has been a problem.


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to