Bruce,

Could you expand on “why” you would want the air to keep running?

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Bruce Verhei <[email protected]>
Sent: Friday, January 12, 2018 10:25:17 AM
To: [email protected]
Subject: Re: Exhaust Air - Paint Booth

Are paint spray operations at this booth supplied by drum or IBC-quantity 
containers located outside the booth? By that I mean as opposed to the more 
common small containers on integral to the hand held spray gun or small inline 
pot.

It’s common to use a flow switch to drop power to pump connected to drum on 
waterflow.

Without this fire can attack hose in booth. Pump sees this pressure drop as 
demand for product, and pumps remainder of drum or IBC (intermediate bulk 
container) into booth. Result from a sprinkler design point of view can be 
operation of dozens of heads outside booth. From occupants point of view 
they’re now in a fast occurring, if not fast spreading, fire producing dark 
smoke. I assume fully sprinklered building.

I’d ask AHJ what they prefer. Total flood dry chem systems require fan shut 
down. But sprinklers do not. But some AHJ’s might require fan shut down. From a 
compliance point of view the AHJ and architect are trying to find a way not to 
count the entire quantity of liquid as being in Use.

As an Alternative Material and Method ruling design, the AHJ has considerable 
sway.

Two questions to resolve early are switch testing and retard setting. 5 seconds 
seems to be adequate to prevent unwanted alarms in my experience.

For the record I would have preferred to leave the fan running. But you should 
call the fire plan reviewer for this project.

Best.

Bruce Verhei

On Jan 12, 2018, at 08:20, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:

I would say “probably” but a detection is faster and certainly more 
conventional.  I would actually defer to the electrician or EE who’s overseeing 
design/installation of building controls and ask them.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 8:16 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Exhaust Air - Paint Booth

Sorry. Yes , spray booth. Flow switch specific to booth.

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Friday, January 12, 2018 9:14:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Exhaust Air - Paint Booth

I assume you mean a spray booth?   Is the flow switch peculiar to sprinklers in 
the booth or will it signal upon flow of any sprinkler in the building in which 
the booth is located?

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 8:12 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Exhaust Air - PaintBoith

Quick question

When using a flow switch to shunt trip a booth, should the exhaust air moment 
be stopped as well?

Get Outlook for iOS<https://aka.ms/o0ukef>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to