To agree with Thom and NFPA 33 I’ll drone on.

As NFPA 33 states, shutdown the ventilation if the listing for the suppression 
system requires it. The total flood dry chemical systems do. The powder is 
light and would otherwise get sucked against the downstream filter. (As one of 
those normal issues when multiple trades are involved this is a common reason 
for failure of inspection of this type of system.) Simplified design is for 100 
lf of air x cross section of booth. So I follow the listing. NFPA  33 is in 
accordance with the listing.

Sprinklered booth. It may be EH2, but this is one time all the heads in the 
design area are going to operate. This is what fire experience shows. Unless 
the just below the roof level is loaded, and fails to operate.

Consider the question of whether the ventilation is a good thing, as it removes 
the products of combustion, vs the ventilation provides a continuous stream of 
fresh oxygen to the fire.

The goal of most life safety features in a building are intended to allow 
people to escape to safety. The fire gases are the direct threat. The are hot, 
choking, poisonous, and vision impairing, by three modes. And the quantity of 
fire gases increase rapidly, and the rate of increase increases, in a tilted 
stepwise manner.

We’ve controlled the rapid expansion of the fire with sprinklers. And the air 
outside the booth will not be what FF’s call hot. Sprinklers again.

But it would still be smokey.

How do we decide. Fire experience. We know that sprinklers with a couple 
exceptions are effective at keeping the fire in the booth.* The failure modes 
have nothing to do with ventilation. Again, as a flammable liquid fire, and 
maybe a car fire, were not extinguishing the fire. We’re confining and cooling 
it while it burns out.

So we know from fire experience that ventilation doesn’t often cause fire to 
leave the booth. And we know that it makes escape easier and safer. It makes a 
safer environment for the FF’s. Plus there is the business continuity benefit. 
While the booth is out of service, and may or may not be headed to the 
recyclers, the rest of the operation should be back in operation next shift. 
Smoke has not damaged everything in the business.

So we leave the fan on.


Pro-point bonus for any lurking fire inspectors. When I first started doing 
booth inspections I didn’t have anyone teach me. So I had to study extra, and 
read the plans in detail. So the first time I got a ladder to go across the top 
of the booth to look at the motor and fan installation the installers blew up 
in anger. What I learned from the installers was that Grainger fouled up and 
sent out the next size smaller motor. What I found the next six months was that 
some how the foul ups were always for a smaller, never larger motor. Eventually 
word got out and this stopped. So just because the plans say 2 1/2 HP, it 
doesn’t mean the installed motor isn’t a 2 HP. You’ve got to look. And AFSA 
moderator, I’m not maligning by name a supplier. Of course Grainger sent 
exactly the motor that booth installers ordered and paid for.

Bruce Verhei

*Exceptions.
Booths are required to have clear space around them; this may be reduced if 
adjacent to non-combustible construction. I admit this as theoretical, without 
personal knowledge. I have found cardboard etc stacked against booths. I 
haven’t seen a fire in this situation. The outside of the booth can be hot 
though.
Roof penetrations through a combustible membrane. These are always tough to get 
right initially. And there is no fire inspection for reroof. And the one head 
most likely to be loaded is the dry head below the roof. But I’ve only seen 
this in an industrial situation, with near continuous spray, through three 
shifts. And the FF’s rapidly put those fires at the roof out. A plant in a 
small town with six volunteers responding in the daytime? I don’t know.

Then fire extending directly from the booth fire. While considering proposing a 
code change  years ago an FM engineer kindly provided me with a series of 
reports on booth fires from their covered properties. All the heads operated, 
all the time. The ones with fire extending out and operating large numbers of 
heads (up to 55) had in common bulk supply from outside the booth. All the fuel 
was pumped into the booth.


On Jan 12, 2018, at 10:29, Larry Keeping 
<[email protected]<mailto:[email protected]>> wrote:

I just took a look at what NFPA 33 says about fire protection and ventilation:

9.2  Ventilation Systems.  Air make-up systems and spray area exhaust systems 
shall remain functioning during any fire condition.

9.2.1*  Where air exhausted from spray areas is recirculated, an interlock 
shall shut down the recirculation of air during any fire condition unless it 
can be demonstrated that shutdown creates a greater hazard.

9.2.2   Air make-up systems, spray area recirculation systems, and spray area 
exhaust systems shall be permitted to be shut down and dampers shall be 
permitted to close where the automatic fire protection system type requires 
that ventilation be discontinued.

Does that should answer the question?

Larry Keeping


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thom Heller
Sent: January-12-18 1:05 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Exhaust Air - Paint Booth

As an AHJ, in my jurisdiction, we would want the exhaust air to remain on 
(removal of products of combustion in the event of a fire) while the make up 
air would be discontinued.  Thom

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 9:41 AM
To: 
[email protected]<mailto:[email protected]>;
 
[email protected]<mailto:[email protected]>
Subject: Re: Exhaust Air - Paint Booth

Bruce,

Could you expand on “why” you would want the air to keep running?

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Bruce Verhei <[email protected]<mailto:[email protected]>>
Sent: Friday, January 12, 2018 10:25:17 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Exhaust Air - Paint Booth

Are paint spray operations at this booth supplied by drum or IBC-quantity 
containers located outside the booth? By that I mean as opposed to the more 
common small containers on integral to the hand held spray gun or small inline 
pot.

It’s common to use a flow switch to drop power to pump connected to drum on 
waterflow.

Without this fire can attack hose in booth. Pump sees this pressure drop as 
demand for product, and pumps remainder of drum or IBC (intermediate bulk 
container) into booth. Result from a sprinkler design point of view can be 
operation of dozens of heads outside booth. From occupants point of view 
they’re now in a fast occurring, if not fast spreading, fire producing dark 
smoke. I assume fully sprinklered building.

I’d ask AHJ what they prefer. Total flood dry chem systems require fan shut 
down. But sprinklers do not. But some AHJ’s might require fan shut down. From a 
compliance point of view the AHJ and architect are trying to find a way not to 
count the entire quantity of liquid as being in Use.

As an Alternative Material and Method ruling design, the AHJ has considerable 
sway.

Two questions to resolve early are switch testing and retard setting. 5 seconds 
seems to be adequate to prevent unwanted alarms in my experience.

For the record I would have preferred to leave the fan running. But you should 
call the fire plan reviewer for this project.

Best.

Bruce Verhei

On Jan 12, 2018, at 08:20, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
I would say “probably” but a detection is faster and certainly more 
conventional.  I would actually defer to the electrician or EE who’s overseeing 
design/installation of building controls and ask them.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 8:16 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Exhaust Air - Paint Booth

Sorry. Yes , spray booth. Flow switch specific to booth.

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Friday, January 12, 2018 9:14:22 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Exhaust Air - Paint Booth

I assume you mean a spray booth?   Is the flow switch peculiar to sprinklers in 
the booth or will it signal upon flow of any sprinkler in the building in which 
the booth is located?

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 8:12 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Exhaust Air - PaintBoith

Quick question

When using a flow switch to shunt trip a booth, should the exhaust air moment 
be stopped as well?

Get Outlook for iOS<https://aka.ms/o0ukef>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to