To further clarify, the material is typically not considered combustible and 
2015 IFC 3006.1 states for Class B ovens that fire prot. is only required when 
the oven contains or is utilized for processing combustible materials.


Craig L. Prahl
Fire Protection Group Lead/SME
JACOBS - CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Prahl, Craig/GVL
Sent: Wednesday, January 24, 2018 2:48 PM
To: [email protected]
Subject: RE: powder coating ovens [EXTERNAL]

Chapter 30 of the IFC deals with ovens/furnaces.  First determine the Class of 
the oven based on its use.

If your process falls into the definition of use for a Class A or Class B oven 
per Section 3006, internal fire protection is needed.

Powder Coating curing ovens are often considered Class B ovens.


Craig L. Prahl
Fire Protection Group Lead/SME
JACOBS - CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Rocci 3 Cetani
Sent: Wednesday, January 24, 2018 1:42 PM
To: 
[email protected]<mailto:[email protected]>
Subject: powder coating ovens [EXTERNAL]

Looking for some guidance on hazard classification for a large oven used for 
curing powder coating and NFPA  86 wasn't much help. Per NFPA 33 powder coating 
booths are OH2 so logically I would think the oven curing the powder coating 
would be OH2.... Thought?


Thanks

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


[email protected]<mailto:[email protected]>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to