Vince, If the mezzanine steel is deep enough and solid it can be the draft curtain.
*Glen Bue**low* *Glen W. Buelow, Inc.* *Fire Protection Design and ConsultingCleveland 330.220.7201 <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* On Thu, Jan 25, 2018 at 8:50 AM, Vince Sabolik <[email protected]> wrote: > Good morning, forum - > > Looking for opinion or code reference. > > Is a draft curtain required? > > ESFR system at roof 25 ft > > Mezzanine at 12 ft, opens out to high roof > > Can standard qr heads be used under the mezzanine without a draft curtain? > > thanks, Vince > > > 11351 Pearl Road / Suite 101 > Strongsville, Ohio 44136 > Phone 440 238-4800 <(440)%20238-4800> Fax 440 238-4876 <(440)%20238-4876> Cell > 440 724-7601 <(440)%20724-7601> > > > * Vince Sabolik * > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >