EXACTLY what I was thinking. I wonder why NFPA just doesn't say to use
QRs to make the draft
curtain go away.
Thanks, Kyle!
On 1/25/2018 9:55 AM, Kyle.Montgomery wrote:
We dealt with this recently where the argument was how to define
“adjacent” sprinklers and whether a mezzanine some 10-plus feet below
the ESFR system should be considered adjacent. I’m not sure if there
was a consensus. But that was a concern because the heads under the
mezzanine were going to be standard response. I don’t see why you
would be worried with QR sprinklers.
See 8.4.6.4.1, where it specifically addresses “where ESFR sprinkler
systems are installed adjacent to sprinkler systems with
STANDARD-RESPONSE sprinklers…”
-Kyle M
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Vince Sabolik
*Sent:* Thursday, January 25, 2018 6:50 AM
*To:* [email protected]
*Subject:* [EXTERNAL] ESFR Stuff
Good morning, forum -
Looking for opinion or code reference.
Is a draft curtain required?
ESFR system at roof 25 ft
Mezzanine at 12 ft, opens out to high roof
Can standard qr heads be used under the mezzanine without a draft curtain?
thanks, Vince
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org