Accessible to view during the 200-lb hydrostatic acceptance testing (YES) (before sofit or wall or ceiling is installed to cover pipe), or accessible permanently (for us, not required).
Andrew Steele Dayton OH Fire Dept. – Fire Marshal. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matt Grise Sent: Thursday, February 08, 2018 3:03 PM To: [email protected] Subject: RE: threaded union fitting Have they provided any codes to back that up? Matt From: Sprinklerforum [mailto:[email protected]] On Behalf Of 321 Sent: Thursday, February 08, 2018 2:01 PM To: [email protected]<mailto:[email protected]> Subject: Re: threaded union fitting I have occasionally been hit with that. The reason is that threaded unions are notoriously prone to leak. I will not use them on anything that can be grooved instead for this reason. I will use them down stream of a drain valve but otherwise try to avoid them. John W. Farabee 561-707-5150 On Thursday, February 8, 2018 1:33 PM, Matt Grise <[email protected]<mailto:[email protected]>> wrote: I recently had an inspector say that all threaded union fittings must be accessible (access panel provided for union behind sheet rock). I have hear that this is a requirement for domestic water piping, but I have never heard about this for fire sprinklers. Does this ring a bell with anyone? Thanks! Matt _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org