Nope...just "It is what it is". 
John W. Farabee
561-707-5150
 

    On Thursday, February 8, 2018 2:01 PM, 321 <[email protected]> wrote:
 

 I have occasionally been hit with that. The reason is that threaded unions are 
notoriously prone to leak. I will not use them on anything that can be grooved 
instead for this reason. I will use them down stream of a drain valve but 
otherwise try to avoid them. 
John W. Farabee
561-707-5150
 

    On Thursday, February 8, 2018 1:33 PM, Matt Grise <[email protected]> 
wrote:
 

  #yiv3981057576 #yiv3981057576 -- filtered {panose-1:2 4 5 3 5 4 6 3 2 
4;}#yiv3981057576 filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 
4;}#yiv3981057576 p.yiv3981057576MsoNormal, #yiv3981057576 
li.yiv3981057576MsoNormal, #yiv3981057576 div.yiv3981057576MsoNormal 
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;}#yiv3981057576 a:link, 
#yiv3981057576 span.yiv3981057576MsoHyperlink 
{color:blue;text-decoration:underline;}#yiv3981057576 a:visited, #yiv3981057576 
span.yiv3981057576MsoHyperlinkFollowed 
{color:purple;text-decoration:underline;}#yiv3981057576 
span.yiv3981057576EmailStyle17 {color:windowtext;}#yiv3981057576 
.yiv3981057576MsoChpDefault {}#yiv3981057576 filtered {margin:1.0in 1.0in 1.0in 
1.0in;}#yiv3981057576 div.yiv3981057576WordSection1 {}#yiv3981057576 I recently 
had an inspector say that all threaded union fittings must be accessible 
(access panel provided for union behind sheet rock). I have hear that this is a 
requirement for domestic water piping, but I have never heard about this for 
fire sprinklers. Does this ring a bell with anyone?     Thanks!    Matt     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


   

   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to