Nope...just "It is what it is".
John W. Farabee
561-707-5150
On Thursday, February 8, 2018 2:01 PM, 321 <[email protected]> wrote:
I have occasionally been hit with that. The reason is that threaded unions are
notoriously prone to leak. I will not use them on anything that can be grooved
instead for this reason. I will use them down stream of a drain valve but
otherwise try to avoid them.
John W. Farabee
561-707-5150
On Thursday, February 8, 2018 1:33 PM, Matt Grise <[email protected]>
wrote:
#yiv3981057576 #yiv3981057576 -- filtered {panose-1:2 4 5 3 5 4 6 3 2
4;}#yiv3981057576 filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2
4;}#yiv3981057576 p.yiv3981057576MsoNormal, #yiv3981057576
li.yiv3981057576MsoNormal, #yiv3981057576 div.yiv3981057576MsoNormal
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;}#yiv3981057576 a:link,
#yiv3981057576 span.yiv3981057576MsoHyperlink
{color:blue;text-decoration:underline;}#yiv3981057576 a:visited, #yiv3981057576
span.yiv3981057576MsoHyperlinkFollowed
{color:purple;text-decoration:underline;}#yiv3981057576
span.yiv3981057576EmailStyle17 {color:windowtext;}#yiv3981057576
.yiv3981057576MsoChpDefault {}#yiv3981057576 filtered {margin:1.0in 1.0in 1.0in
1.0in;}#yiv3981057576 div.yiv3981057576WordSection1 {}#yiv3981057576 I recently
had an inspector say that all threaded union fittings must be accessible
(access panel provided for union behind sheet rock). I have hear that this is a
requirement for domestic water piping, but I have never heard about this for
fire sprinklers. Does this ring a bell with anyone? Thanks! Matt
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org