I thought about this some since. When 13-R and residential sprinklers showed up 
they were only available in 155-165f range. And a few times we had a spot that 
required an intermediate head. So we used an SSP intermediate head. It’s what 
was available. 

Best.

Bruce Verhei 



> On Feb 8, 2018, at 07:29, Roland Huggins <rhugg...@firesprinkler.org> wrote:
> 
> Ok put your skates on if your going to go out on the ice with me.  It’s a 13R 
> building.  You want to use a type of sprinkler not available in the 
> residential family so are applying 13 in so far as it is applicable (aka as 
> defined by outside the dwelling unit).  QR spray sprinklers are accepted for 
> dwelling units while applying the LH design basis (as per 13). If we can 
> apply the hybrid design basis fro OH in a 13R system, why not for LH?  That’s 
> my trail of dots.  Since it is not explicitly drawn in the standard, discuss 
> with the AHJ.
> 
> 
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.    
> Dallas, TX
> http://www.firesprinkler.org
> 
> Fire Sprinklers Saves Lives
> 
> 
> 
> 
>> On Feb 7, 2018, at 4:01 PM, Fpdcdesign <fpdcdes...@gmail.com> wrote:
>> 
>> I wasn't sure I could justify these rooms as outside the dwelling unit when 
>> the crux of my argument is that the entire building is a dwelling unit. 
>> 
>> I told the owner that if we went with institutional sprinklers, we would 
>> need to change the design to NFPA 13, at an additional cost. Suddenly the 
>> requirement went away. 
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-553-3553 (fax)
>> 860-608-4559 (cell)
>> 
>> 
>>> On Feb 7, 2018 at 6:19 PM, <Roland Huggins> wrote:
>>> 
>>> There’s also the hybrid room design method for outside the dwelling uniting 
>>> 13R: 7.2.3.1 (so deemed a more demanding design basis) that could be 
>>> applied.
>>> 
>>> 
>>> Roland Huggins, PE - Senior VP Engineering
>>> American Fire Sprinkler Assn.    
>>> Dallas, TX
>>> http://www.firesprinkler.org
>>> 
>>> Fire Sprinklers Saves Lives
>>> 
>>> 
>>> 
>>> 
>>>> On Feb 7, 2018, at 6:43 AM, Fpdcdesign <fpdcdes...@gmail.com> wrote:
>>>> 
>>>> I am working on a group home which is being designed as NFPA 13R (2010). 
>>>> The owner is requiring instutional sprinklers in the bedrooms only. I 
>>>> cannot find any institutional residential sprinklers, so we are going to 
>>>> have to use commercial QR instutional sprinklers. Section 6.2.1.3.1 states 
>>>> that when using QR sprinklers, the density/area shall be a minimum of 0.10 
>>>> gpm/sqft over the entire dwelling unit. In this situation, based on the 
>>>> NFPA 13R definition of dwelling unit, we would need to calculate 0.10 
>>>> gpm/sqft over the entire 2 story house. That doens't make sense. Am I 
>>>> missing something?
>>>> 
>>>> Todd G Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, CT
>>>> 860-535-2080 (ofc)
>>>> 860-553-3553 (fax)
>>>> 860-608-4559 (cell)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@lists.firesprinkler.org
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________ Sprinklerforum mailing list 
>>> Sprinklerforum@lists.firesprinkler.org 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list