I understand hazard classification is based on the fire load and the rates of 
heat release of materials and processes being protected.  With those 
parameters, we choose hazard classification and provide a density for say 
Ordinary Hazard Group II  - 0.20 gpm/sqft over a design area 1500 sqft to 
contain a fire (less if with quick response reduction).  I have inspected many 
schools and visited their shop classes over the years.  Materials, dust, paint 
spray booths and the storage of student projects well exceed the 1500 sqft 
design areas, so the hazard is present.  NFPA 13 - 5.3.1 Ord Haz I may easily 
be picked with no quantitative amounts stated.  But, the appendix A.5.3.2 
suggests as explanatory reference that Wood Product Assembly and Wood Machining 
are Ord Haz II with no distinction in commercial or educational use.  Pre - 
1991 listed Wood Machining as Ord Haz III.  I mainly wanted to get the forums 
input/debate on how others classified this hazard. 


Sincerely,
Joe Kuerzi Jr., SET
   

    On Saturday, April 21, 2018, 6:52:30 PM EDT, Mark.Phelps 
<[email protected]> wrote:  
 
 I wasn't arguing for light hazard. Only that in my opinion it should be 
ordinary 1 and not extra as a commercial shop would be. We at Aero have 
installed sprinklers in well over 300 schools and had to argue with both AHJ's 
and consultants (present company excluded) over things like running 8" fire 
lines into classroom buildings. It's a horrible waste of school funding 
resources. 

Mark at Aero602 820-7894
Sent from my iPhone
On Apr 21, 2018, at 4:23 PM, Steve Leyton <[email protected]> wrote:



All true, but apples to oranges. A commercial woodshop is a step above a school 
woodshop. We do an awful lot of schools work and you would be amazed at what a 
modern high school woodshop looks like Mark. Multi station dust collectors are 
the norm. It's definitely at least an ordinary hazard. A commercial wood shop 
is  Extra Hazard, the debate there being whether it's Group 1 or Group 2.


Sent from my Verizon, Samsung Galaxy smartphone

-------- Original message --------From: "Mark.Phelps" 
<[email protected]>Date: 4/21/18 2:15 PM (GMT-08:00) To: 
[email protected]: Re: [EXTERNAL] Re: Wood Shop 
Classroom Classification of Hazard 
The one thing I would add to this is to compare the fire loading between a 
commercial cabinet/wood shop and the classroom environment. A typical 
commercial shop would have sheet goods and lumber inventory for hundreds of 
cabinets, as well as hundreds of boxed finished goods. A typical wood shop 
classroom environment would have nothing close to that. 

Mark at Aero602 820-7894
Sent from my iPhone
On Apr 21, 2018, at 3:34 PM, Steve Leyton <[email protected]> wrote:



NFPA 13 speaks to the nature of the use, not just the label of a particular 
building or compartment. If it has fire load, or processes, or byproduct of 
those processes that make it more hazardous, then it's more hazardous. Out here 
in California were used to fire protecting vocational technology and science 
and shop (auto, wood, metal) classrooms to the higher hazard classification 
because they may contain pressurized natural gas, welding or soldering, 
flammable liquids, open burners higher levels of dust, etc. 
I agree with you - stay the course.
Steve L.

Sent from my Verizon, Samsung Galaxy smartphone

-------- Original message --------From: joseph kuerzi 
<[email protected]>Date: 4/21/18 11:42 AM (GMT-08:00) To: 
[email protected]: Wood Shop Classroom 
Classification of Hazard 
I interpret the hazard classification of 3000sqft Wood Shop Classroom 
(High/Middle School) as Ordinary II - Wood Machining/Wood Product Assembly.  I 
was told that I was incorrect in my classification since it was a classroom and 
not a Woodshop Facility.  I can not find justification in the standards to down 
grade the hazard classification to Light or Ordinary I  just because the room 
is a classroom.  Am I missing something?  NFPA 13, 2010ed and IBC 2012

Sincerely,
Joe Kuerzi Jr., SET

           Certified Protection Services LLC
                  175 Sky Aire Rd. NW 
                   Corydon, IN 47112

 Fire Protection & Water Back-flow Prevention Systems
   Installation, Maintenance, Repair, & Inspections

Contact - Joseph C. Kuerzi Jr., SET
812-738-2970 office
502-551-8530 mobile *preferred
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=GV9x52NVphDNsWHM5QokaLumr6hpYXTeynUOAypTGXk&s=S4pTAkCBlvSSlKqf_9PKE9CDSPCxOW775TQzzEPe0Ac&e=


_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=VxRj6csysDJib4c298RMrq49ChSjYARyTwtWvkzzbKA&s=K39Gf4f7sziUCP7yys1-tj7ekZJBCY4pnzPqJdoLg8c&e=

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to