Ok thanks Steve

Tony


From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton
Sent: Thursday, April 26, 2018 2:16 PM
To: [email protected]
Subject: RE: main drain flows

Right.  And also, the flow rate is a false metric.  Say you open a 2" main and 
flow it at 75 PSI residual.  You get ... a LOT of water per minute, but it's 
only for about 15-20 seconds in a main drain test.   In Southern California 
we've been wrestling with environmental regulations for 6 or 7 years and we're 
not allowed to let sprinkler water run off to storm UNLESS the storm drain 
system is fitted with sand/oil interception or filters or there's bio-retention 
on the site or ... omigosh, it's a total pain.   So this is a panacea fix - 
since we started specifying this arrangement, all the bad people have gone away 
and we've never heard back from anyone that there's been an issue with overflow 
or splashing or any other issues.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Thursday, April 26, 2018 2:11 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: main drain flows

Tony:

What Steve is trying to say in his normal straight to the point way, is that a 
4" drain will normally handle the 250 to 300 GPM max flow you get from a 2" 
main drain test. That is if your water company isn't providing flows over 90 
PSI residual. Anything over 320 gallons exceeds 32 ft per second velocity and 
it takes more pressure to exceed that.

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 5:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: main drain flows

They are looking for the GPM flows out of our main drain during a main drain 
tests. Since a lot of water is going to be released during the test they want 
to make sure the sanitary sewer can handle all the water with the main drain 
fully open under city pressure.

Tony


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Steve Leyton
Sent: Thursday, April 26, 2018 1:53 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: main drain flows

Tell them you want a hub drain with a self-priming 4" trap.  It'll resolve both 
1ΒΌ" and 2" main drain discharges.

Steve

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 1:51 PM
To: 
[email protected]<mailto:[email protected]>
Subject: main drain flows

Long time reader, first time writer.....actually not that long I'm a fairly new 
designer. We have a jurisdiction where they require the main drain to drain to 
a sanitary sewer and the contractor is asking what the flows will be so they 
can size their SS line accordingly. The sprinkler system hasn't been designed 
yet and they said they need to know right now so they can finish their design 
and submit for permit. Is there a way to figure this out (or get a ball park) 
just based off city water flow numbers?

Thank you

Tony