Must have been LinkedIn Nicky.
That K  ( kPa metric ) looks like Coefficient of Discharge = 0.73.
If it's the angle valve I would use 0.62.
If it's the discharge outlet I would use 0.90.
This results in:
K=52.9 and 76.8 ( kPa metric ) respectively.

I always love hearing about how other parts of the world do sprinklers so thanks for that.
The 'isolate' valve you explain is interesting!

Brad


Quoting Nicky Marshall <[email protected]>:

From a LinkedIn or sprinkler forum post sometime in the past, there was advice given to simply use Q=K*sqrt(P)
K of 62.5 ( kPa metric ) for 50mm/2” valve
P is the town main static pressure
This seems to work well for us - it gives the flow rate that we advise the drain needs to handle for a water supply ‘drain’ test.

We send this to storm water as we place an isolate valve above the alarm valve so that ‘dirty’ system water is kept in the system and this is fresh town main drinking water.

For drainage of sprinkler system we have a 100mm/4” drain to the sewer.
The sewer often can’t handle the volumes of the water supply ‘drain’ test which is why we split it.
Hope that helps

Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2 Mobile: +64 (0)21 433 488 Email: [email protected]<mailto:[email protected]> Skype: nicky-marshall Web :www.protechdesign.co.nz Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, Redwood Village, Blenheim 7242, NZ

“I always wondered why somebody doesn't do something about that. Then I realised I was somebody” Lily Tomlin

From: Prahl, Craig/GVL <[email protected]>
Sent: Friday, 27 April 2018 9:20 AM
To: [email protected]
Subject: RE: main drain flows

The system design criteria has no bearing on what can be discharged from the main drain.

You have a city residual pressure flowing through your riser and out your system valve’s 2” drain outlet. What comes out will depend on what’s coming in and the system pressure losses resulting from a specific flow though the riser assembly and out the drain.



Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | [email protected]<mailto:[email protected]> | www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:[email protected]] On Behalf Of Phillips, Mark
Sent: Thursday, April 26, 2018 5:10 PM
To: [email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: main drain flows

Tony
You should be able to do a rough calculation that will give you your system demand. I would use that information to let them figure out their own size.

Its just an estimate and I would reiterate that to them over and over. You cannot supply final information until system is designed completely.

[cid:[email protected]]




[cid:[email protected]]

Mark​



Phillips


Vice President of Fire Protection

,

Kirlin Carolinas, LLC



t: 919-526-1584<tel:919-526-1584>

 |

m: 919-610-0490<tel:919-610-0490>


[email protected]<mailto:[email protected]>

 |

https://kirlingroup.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__kirlingroup.com_&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=LPim5_1wzEKYP6VrPcaGQS-escStiDnU-keCJjkf_os&s=0Uqd20RKMZj61YJrvUMSgZlwyiG2b6y1ilg9m9Azhb8&e=>


8000 Brownleigh Dr

,

Raleigh

,

NC



27617



[cid:[email protected]]<https://urldefense.proofpoint.com/v2/url?u=https-3A__twitter.com_KirlinGroup&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=LPim5_1wzEKYP6VrPcaGQS-escStiDnU-keCJjkf_os&s=oBw_rBJN7E9kZGg-EVHMuNFmLNmAKkFjwuHcf_hlJK4&e=>


[cid:[email protected]]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_kirlinllc&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=LPim5_1wzEKYP6VrPcaGQS-escStiDnU-keCJjkf_os&s=eQs-Ijjpriw_vM5kET6RBV441Kxy5W1MAy07ZRFztyQ&e=>


[cid:[email protected]]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_company_133201_&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=LPim5_1wzEKYP6VrPcaGQS-escStiDnU-keCJjkf_os&s=f-Q7PDCBQXgXFWCye7PpGt255HoLrCAgGVvQTuhldqM&e=>





From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 5:03 PM
To: [email protected]<mailto:[email protected]>
Subject: RE: main drain flows

They are looking for the GPM flows out of our main drain during a main drain tests. Since a lot of water is going to be released during the test they want to make sure the sanitary sewer can handle all the water with the main drain fully open under city pressure.

Tony


From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Steve Leyton
Sent: Thursday, April 26, 2018 1:53 PM
To: [email protected]<mailto:[email protected]>
Subject: RE: main drain flows

Tell them you want a hub drain with a self-priming 4” trap. It’ll resolve both 1¼” and 2” main drain discharges.

Steve

From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 1:51 PM
To: [email protected]<mailto:[email protected]>
Subject: main drain flows

Long time reader, first time writer…..actually not that long I’m a fairly new designer. We have a jurisdiction where they require the main drain to drain to a sanitary sewer and the contractor is asking what the flows will be so they can size their SS line accordingly. The sprinkler system hasn’t been designed yet and they said they need to know right now so they can finish their design and submit for permit. Is there a way to figure this out (or get a ball park) just based off city water flow numbers?

Thank you

Tony




________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to