I did find the 60” rule in FM Global data sheet 1-12. So, I guess my question 
is this:

If the product (tile) is UL-Listed (not just FM-Approved) and I meet the 
requirements of NFPA 13, am I technically REQUIRED to meet the FM Data sheet 
guidelines?

Does anyone know if the testing (actual or theoretical) suggests that the 
sprinklers will fail if placed higher than 60” above these ceilings? Or is it 
just the case of “we haven’t done the testing to prove it will work at greater 
than 60 inches”? I’m just trying to understand why there would be an issue with 
having them higher.

Also, where do you find the “light hazard only” rule? I found a white paper 
that mentioned that, but I haven’t found that in the code or listings so far.

Thanks for your help.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Timothy Goins
Sent: Thursday, May 31, 2018 9:26 AM
To: [email protected]
Subject: [EXTERNAL] Re: Drop-Out Ceiling Tiles

Light hazard only and yes 60" rule went into effect a few years ago.

Thermo-Tile is the only band I know of.

King and Company
PO Box 10
Clarksville AR 72830
United States of America
+1 (800) 643-9530
http://www.thermo-tile.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.thermo-2Dtile.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=w3H0bYFuZwg0xc8Bp8xZ9lZWIW0yiE28vGQX2uzaVWM&s=jRFH8sdzEgA0MBtLvMxRXhx27Pm-gs0STZ5ZJhp3ZB8&e=>

And I will give them one heart, and I will put a new spirit within you; and I 
will take the stony heart out of their flesh, and will give them an heart of 
flesh
Eze 11:19

On May 31, 2018, at 11:00 AM, Kyle.Montgomery 
<[email protected]<mailto:[email protected]>> wrote:
I’ve been searching around a little bit, but figured I would ask here, anyone 
have experience with installing these under sprinklers?

I’m working with an architect whose client needs to install these polystyrene 
ceiling tiles that have been tested to drop-out in the case of a fire. They’re 
not doing it to try to save costs, apparently the spec for the product they 
assemble requires a “clean” environment which drives this.

I’m having trouble finding good information about this. The NFPA requirements 
are pretty straightforward, but I’m seeing some conflicting issues in some of 
the other information I can find:


1.       NFPA 13 does not permit QR heads above these ceilings (unless the 
ceiling is specifically listed for them), yet some of the other information 
I’ve found suggests that they can only be used in light hazard areas.

2.       I’ve seen some information suggesting that the sprinklers need to be 
within 60” of these ceilings, but NFPA 13 makes no mention of that. Is that an 
actual requirement?

Thanks guys. Any info helps.

-Kyle M
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=w3H0bYFuZwg0xc8Bp8xZ9lZWIW0yiE28vGQX2uzaVWM&s=-gAB2ui7vl8ASUrpS4mIvhxslgDpFJeza7U3gWBvsio&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to