My best guess on why 5' max higher than they would be at the drop out level-- the higher the ceiling the longer the activation time no matter what fire growth rate is full scale tested. In this case there is an additional delay due to the sprinklers not being "sensitive" to the fire growth rate from the point of ignition. They might have established pass/fail criteria for the delay (and subsequent increase in heat release rate at activation. They might have tested 4,5,and 6 feet above and got delay times that 'passed', but the 6 foot 'failed'.

Brad

Quoting Timothy Goins <[email protected]>:

Light hazard only and yes 60" rule went into effect a few years ago.

Thermo-Tile is the only band I know of.

King and Company
PO Box 10
Clarksville AR 72830
United States of America
‭+1 (800) 643-9530‬
http://www.thermo-tile.com

And I will give them one heart, and I will put a new spirit within you; and I will take the stony heart out of their flesh, and will give them an heart of flesh
Eze 11:19

On May 31, 2018, at 11:00 AM, Kyle.Montgomery <[email protected]> wrote:

I’ve been searching around a little bit, but figured I would ask here, anyone have experience with installing these under sprinklers?

I’m working with an architect whose client needs to install these polystyrene ceiling tiles that have been tested to drop-out in the case of a fire. They’re not doing it to try to save costs, apparently the spec for the product they assemble requires a “clean” environment which drives this.

I’m having trouble finding good information about this. The NFPA requirements are pretty straightforward, but I’m seeing some conflicting issues in some of the other information I can find:

1. NFPA 13 does not permit QR heads above these ceilings (unless the ceiling is specifically listed for them), yet some of the other information I’ve found suggests that they can only be used in light hazard areas. 2. I’ve seen some information suggesting that the sprinklers need to be within 60” of these ceilings, but NFPA 13 makes no mention of that. Is that an actual requirement?

Thanks guys. Any info helps.

-Kyle M
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to