One way to mitigate this is to have multiple smaller valves that operate 
sequentially. In other words, you can use maybe a 2-1/2” valve and a 4” valve 
to replace a single 4” valve (for example). You set the smaller valve to open 
at 90% full and the 4” valve to open at 80% (I’m just pulling random numbers). 
That way, under normal fill conditions you just have the small valve open to 
refill the tank. But in a fire scenario when the level drops faster than the 
smaller valve can keep up with, then the bigger valve opens.

To answer the original question: Yes, you can reduce the tank size based on 
being able to refill it, but as Craig mentioned, there are some caveats. I 
assume the tank is a break tank feeding a fire pump,  but does that fire pump 
feed only sprinkler systems? Does it feed a standpipe with hose valves? Does it 
feed hydrants on site? Would whatever you are protecting normally require any 
redundancy, or is the tank being provided solely because the available water 
supply is insufficient?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kenneth Berman
Sent: Wednesday, June 13, 2018 2:14 PM
To: [email protected]
Subject: Re: [EXTERNAL] Ground Storage tank

When I do inspections in the "country", and there's a storage tank with 
altitude valve, control valves are often partially closed to throttle the flow. 
When the 4" valve opens to fill the tank, it drops the pressure so much there's 
no water for toilets and sinks. Building owners, or occupants, "fix" the 
pressure problem long after the initial construction and acceptance tests. I 
can't count on the water main to resupply during demand.

On Wed, Jun 13, 2018 at 1:41 PM, Prahl, Craig/GVL 
<[email protected]<mailto:[email protected]>> wrote:
When sizing a water storage tank for fire protection do no forget the IFC code 
requirement for Fire Flow in section 507.  It's an additional water supply 
requirement apart from sprinkler flow.  This is especially critical if the 
municipal supply is not sufficient to meet the required flow rates as dictated 
by the Approved Method for determining Fire Flow.

But to your question.  It sounds like you want to take credit for the incoming 
water supply flow rate to reduce your storage capacity, correct?

If that is the case, there are a few things that you must consider and you must 
get approval from the AHJ and any insurer.
1. Is the municipal flow rate guaranteed to be available 24/7/365?
2. Will the local Fire Code official and the owner's insurer approve of the 
concept.

In theory you could take the credit and use the municipal supply as a buffer 
against the increased tank size but at some point in time you reach a point 
where you could consume at a rate greater than can be made up especially with 
the fire flow demand rate.  We've only been successful in incorporating this 
concept on one occasion.  Typically, our projects tend to be high value and 
high hazard and the lack of an adequate water supply for fire suppression and 
firefighting is not something that the AHJs or Insurers were willing to 
compromise on.  But when the owner asks, we'll oblige and ask the question of 
the AHJ.

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=qQd135zn_TMkTxYr5FwwmCd5uxlVCrSzB9-BXIYyT5Q&s=dbBIHoPyHME8yMsElaCwcYwl_XEFzKQ0dpBtYLiNMkI&e=>

-----Original Message-----
From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of George W. Henderson
Sent: Wednesday, June 13, 2018 2:29 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Ground Storage tank

  I am attempting my first participation.
We have the need for a ground storage tank.  The MUD cannot supply volume or 
pressure.  We size the tank to satisfy the code water supply duration.  This 
tank about 200,000 gallons, Is it allowed to use the the MUD water supply 
refill to reduce the size of the tank?

--
George W. Henderson VP  RME 0054-GD
Eagle Automatic Fire Sprinkler Inc
1777 Upland Dr.  #107
Houston, TX  77043
713-939-0708 (office)
832-435-1393 (cell)

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=IjGuE8b8uSlg8Jr-VSUCrW37fKKQ-DnT0-mJlALaPVg&s=fqpzgBBqeBWkNGsyB3C517JIsF-D3XkgEBUwFFDmltM&e=
________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=qQd135zn_TMkTxYr5FwwmCd5uxlVCrSzB9-BXIYyT5Q&s=FnfxYhPapMwJGrbMGmafmZc84gn2hC2pZWH6XVVvFcI&e=>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to