I've got a building that is two towers with a parking garage in between.
One tower is 11 floors and is a high rise, with two standpipes. The other
tower is 9 floors and isn't a high rise, with three standpipes. The AHJ has
said that because the towers and garage are all connected, the tower that
isn't a high rise is considered a high rise with respect to standpipe
calculations. I had originally considered my calc to be 750 gpm for the two
standpipes in the high rise, them being automatic wet, and 1000 gpm for the
three in the non-high rise, them being manual wet. Does it make sense that
the AHJ has said it is one building with 5 standpipes, and to do a 1000 gpm
calc with the two standpipes in the high rise and one in the non-high rise
(the fire pump is in the non-high rise)?