2015 IBC/IFC FIRE AREA. The aggregate floor area enclosed and bounded by Fire 
Walls, Fire Barriers, Exterior Walls or Horizontal Assemblies of a building. 
Areas of the building not provided with surrounding walls shall be included in 
the fire area if such areas are included within the horizontal projection of 
the roof or floor next above. 


Fire Walls etc are italicized in printed code, meaning they’re code defined 
terms. 

But this is work product of the architect, as approved by the building 
department. Plans for a building permit that do not show any Fire Area’s, 
except for a Fire Area that includes the entire building, are not accepted for 
submittal. 

Without this information even the fire plans reviewer can’t start work on their 
part of building permit review. If I had questions conflict between shown Fire 
Areas, allowable areas calculations or some other basic problems with submitted 
plans expect me representing fire to stand at the building reviewers desk to 
talk about it. That’s what elevators are for.

You can’t do a review down to say, talking about detection for fire/smoke 
dampers if the basic design is flawed or incomplete.

Best.

Bruce Verhei 

> On Jun 29, 2018, at 05:55, Ed Kramer <[email protected]> wrote:
> 
> I’m not sure how this plays into this, if at all. 
>  
> Section 7.10 and subsections tell us how many standpipes to calc and how much 
> water should flow through each.  Annex section A.7.10.1.1 says “If a water 
> supply system supplies more than one building OR MORE THAN ONE FIRE AREA, the 
> total supply can be calculated based on the single building OR FIRE AREA 
> requiring the greatest number of standpipes.”  Capitalization added by moi.   
>  Since I’m not a IBC kind of guy, how do we define a “fire area”?
>  
> Ed Kramer
> Bamford Fire
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steele, Andrew
> Sent: Friday, June 29, 2018 7:24 AM
> To: '[email protected]' 
> <[email protected]>
> Subject: RE: High Rise and Non-High Rise Standpipes
>  
> First thought, is it really ONE building, or three (or two, etc. based on 
> firewalls).  This is a question for the Architect and/or the Building 
> Official, not the FM.   The FM may not know, particularly if they were not 
> involved in the structural review/permitting process.  Or they may know, and 
> it is in fact one building, a high-rise.
>  
> Andrew Steele
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Matt Grise
> Sent: Friday, June 29, 2018 12:58 AM
> To: [email protected]
> Subject: RE: High Rise and Non-High Rise Standpipes
>  
> A friendly “please provide the code you are looking at” email followed by an 
> in-person meeting could be just what the doctor ordered! If what they are 
> asking for does not strictly follow the code, you should be able to ask for a 
> change order.
>  
> I will quote one of my preferred sources of info on standpipes - Mr. Señor 
> Steve Leyton: “the standpipe system is exclusively for the use of the fire 
> department, so give them what they ask for” **
>  
> I will also give you one of my favorite quotes from one of my very favorite 
> sources - [me] : “good luck getting the city council to override a fire 
> marshal who says he needs this for the safety of his fire crews and the 
> people in the building”
>  
> Matt
>  
> **I realize Señor Leyton already made a very good comment. And I hope it goes 
> without saying that my opinion of Steve’s opinion could not possibly hope to 
> have any authority or relation to any of the NFPA work that Steve does.
>  
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of James Litvak
> Sent: Thursday, June 28, 2018 12:44 PM
> To: [email protected]
> Subject: High Rise and Non-High Rise Standpipes
>  
> I've got a building that is two towers with a parking garage in between. One 
> tower is 11 floors and is a high rise, with two standpipes. The other tower 
> is 9 floors and isn't a high rise, with three standpipes. The AHJ has said 
> that because the towers and garage are all connected, the tower that isn't a 
> high rise is considered a high rise with respect to standpipe calculations. I 
> had originally considered my calc to be 750 gpm for the two standpipes in the 
> high rise, them being automatic wet, and 1000 gpm for the three in the 
> non-high rise, them being manual wet. Does it make sense that the AHJ has 
> said it is one building with 5 standpipes, and to do a 1000 gpm calc with the 
> two standpipes in the high rise and one in the non-high rise (the fire pump 
> is in the non-high rise)?
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org