Sounds like the designer is a little confused.  The PIV won't prevent flow
unless it's closed and let's hope it's not closed.

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772
 


[email protected]
www.fire-design.com

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Prahl, Craig/GVL
Sent: Monday, July 9, 2018 11:27 AM
To: [email protected]
Subject: RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

When that reason was presented to the designer they stated that's what the
PIV on the UG was for.  To isolate the UG from the AG system.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 |
[email protected] | www.jacobs.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Denhardt
Sent: Monday, July 09, 2018 10:39 AM
To: [email protected]
Subject: [EXTERNAL] RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in
supply 

Exactly.

Thanks,
John
 
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Richard Carr
Sent: Monday, July 9, 2018 10:38 AM
To: [email protected]
Subject: RE: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

I have always thought the check valve was to so the FDC did not pump up the
underground.

Richard M. Carr, SET
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NC  28731

[email protected]
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile






-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Prahl, Craig/GVL
Sent: Monday, July 09, 2018 10:34 AM
To: [email protected]
Subject: 2013 NFPA 13, Figure A.8.16.1.1 Check valve in supply 

Having a discussion with a designer concerning a manifolded riser assembly
which has a dry pipe system and wet pipe system as shown in 2013 NFPA 13,
Figure A.8.16.1.1.  The question is the purpose of the check valve in the
portion below the split at the manifold.  Their FDC is piped in accordance
with the detail.  The designer says the check valve in the vertical is not
needed because they are on a non-potable water supply and they have a PIV
outside.

Thoughts, opinions?

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 |
[email protected] | www.jacobs.com

____________________________________________________________________________
____________

NOTICE - This communication may contain confidential and privileged
information that is for the sole use of the intended recipient. Any viewing,
copying or distribution of, or reliance on this message by unintended
recipients is strictly prohibited. If you have received this message in
error, please notify us immediately by replying to the message and deleting
it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEe
xU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=M
Iyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYv
i4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEe
xU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=M
Iyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYv
i4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=OgZOSER8c1RLeytEe
xU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=M
Iyv3E2h5_6bDxuz4mKDKbGlpUL2hNWwltHyMeMVZsY&s=rP1gn3mNbmZ2b-Rjkl4sdxzEZTemTYv
i4gejV-TbxNY&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to