Thanks!

On Fri, Jul 13, 2018 at 11:47 AM, <tston...@comcast.net> wrote:

> Pipe arrangement is not mentioned in 11.2.23.4.2.
>
> I single line of sprinklers.
>
>
>
> Tim
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Fire Design
> *Sent:* Friday, July 13, 2018 2:07 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: NFPA 13 RESIDENTIAL Exterior Corridor
>
>
>
> Thanks guys... regarding 11.2.3.4.2. I always thought that was only good
> for a single row meaning all the sprinklers were directly on the line. In
> this case the sidewalls are fed from armovers coming from a looped main.
> Would this still apply?
>
>
>
>
>
>
>
> On Fri, Jul 13, 2018 at 10:28 AM, <tston...@comcast.net> wrote:
>
> Anthony,
>
>
>
> Look at 11.2.3.4.2.
>
>
>
> Regards,
>
> *G. Tim Stone*
>
>
>
> *G. Tim Stone Consulting, LLC*
>
> *NICET Level III Engineering Technician*
>
> *Fire Protection Sprinkler Design*
>
> *and Consulting Services*
>
>
>
> *   117 Old Stage Rd. - Essex Jct., VT. 05452*
>
> *CELL: (802) 373-0638   TEL: (802) 434-2968*
>
>              tston...@comcast.net
>
>
>
>
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Fire Design
> *Sent:* Friday, July 13, 2018 1:21 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* NFPA 13 RESIDENTIAL Exterior Corridor
>
>
>
> Hi Guys,
>
>
>
> I'm working on an apartment complex that is being designed per NFPA 13
> standards (2016). All the rooms open from an exterior covered corridor that
> is 6 ft wide, combustible, and therefore requires sprinklers. I will need
> to use dry sidewall sprinklers for this and I see there are no residential
> dry sidewall sprinklers with an intermediate temperature rating. (TYCO
> makes one that is good to 155F) So, this means I will need to go with quick
> response sprinklers in a project that can otherwise be designed per the
> residential section of '13. Now, I figured being a corridor I would only
> need to calculate 5 or 7 sprinklers and that figure comes to mind but now
> the only reference I can find for that is for the room design method which
> I cannot use in this case since it's open to the exterior and it's not
> really a single row of sprinklers - they are fed from the interior main
> which is looped. If I cannot find a residential dry sidewall sprinkler good
> for 200F does this mean I will need to calculate the full design area? I
> feel like I'm overlooking something critical here but I've already been
> through chapters 11 and 23 page by page and I cannot find anything that
> will allow a smaller design area.
>
>
>
> Any help is appreciated - I don't want to pull the trigger on this when I
> have this nagging feeling that I'm forgetting something.
>
>
>
> -Anthony
>
>
>
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>
> Virus-free. www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>  Virus-free.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
> <#m_-419996947302144767_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to