We’ve done several as OH 2 as well.

But I have always wondered what the realistic adequate level of protection 
would be. The ones we usually deal with have partial-height partitions with 
“burglar bars” separating the units, which allows the heat to spread across the 
deck relatively unimpeded. I’ve wondered if this would activate adjacent 
sprinklers before the adjacent units start to catch fire. And I’ve wondered if 
QR or SR sprinklers are better (or if it even makes a difference).

Is anyone aware of any fire modeling or burn tests done for these types of 
units?

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Thursday, July 26, 2018 1:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Self storage warehouses

They will allow car storage with fuel in the tank.
Metal partitions will easily transmit heat to the adjacent unit.
No propane tanks.
Corp allowed to store overflow stock or equipment.
40,000 SF in low bay.
Corridors will have drop ceilings with pendant sprinklers.


Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Thursday, July 26, 2018 3:39 PM
To: Sprinklerforum
Subject: Re: Self storage warehouses

Make sure they have restrictions on things like rubber tires, flammable 
liquids, etc.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)


On Jul 26, 2018 at 3:31 PM, <Art Tiroly<mailto:atir...@atcofirepro.com>> wrote:
Storage units 200 -600 SF per unit covered by metal screen at 10 Ft. AFF with 
metal sided partitions.
Household goods, mattresses, foam  cushions on sofas. Class 3-Class A plastic.
Roof sprinklers at 14FT is a pipe schedule system from 1956.
This is a change of occupancy.

The existing pipe schedule system is not adequate for the hazard.
The sprinkler system should be revised and brought up to NFPA design density.
Is the appropriate design based on Class A plastic or something less?
I could not find anything in archives.

Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell


[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.avast.com_sig-2Demail-3Futm-5Fmedium-3Demail-26utm-5Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-26utm-5Fcontent-3Demailclient-26utm-5Fterm-3Dicon&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7zniC7VUGZq57TG45yp1cM74BukPq_ZegEODRVtJyVU&s=ENfjhkYHPLOuS6kh-cyMGYTB18HxoZX0bKxn1jqiq0Y&e=>

Virus-free. 
www.avast.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.avast.com_sig-2Demail-3Futm-5Fmedium-3Demail-26utm-5Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-26utm-5Fcontent-3Demailclient-26utm-5Fterm-3Dlink&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=7zniC7VUGZq57TG45yp1cM74BukPq_ZegEODRVtJyVU&s=hUUfi2la-W6hqkDPS1AvTGajbu7C6bRJy9E5FoAdTL8&e=>

_______________________________________________ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>