We produce flow/pressure curves. Then we select a point on that curve. Once 
we’ve selected a design flow point, does the rest of the curve matter. I 
wouldn’t adjust the curve at all. 

Best.

Bruce 

> On Aug 8, 2018, at 15:47, Mark Sornsin [FAR] <[email protected]> wrote:
> 
> It’s clear there are many ways to do it and thus it depends on who’s calling 
> for it.
>  
> IMHO, if there is an engineer of record specifying this, then they should do 
> the work themselves.  I.e.:
> 1.        evaluate the water supply (like conduct and/or observe the actual 
> test)
> 2.       Investigate the source – is it a pumped supply or gravity only, or 
> whatever
> 3.       Identify normal low pressures.  E.g. many small towns up north 
> reduce their tower elevations in winter to reduce freeze potential.  That 
> reduced static pressure should be used regardless of the result of a summer 
> flow test.
> 4.       Identify situations unique to that location – such as a nearby user 
> that has regular high demand flows that significantly reduce the water supply 
> available at your site.
>  
> So you might have a summer test of 60psi static  flowing 1,500 gpm at 40 psi. 
>  But after investigating the above, you learn the static pressure drops 10 
> psi every winter.  So the adjusted flow test would be 50/1500/30.  A line 
> parallel and below the summer test because that’s how the test would look if 
> conducted in the winter.  The slope of the line is unique to the piping 
> arrangement up to the point of the flow test. This is why I don’t necessarily 
> agree with applying a 10% reduction that creates a non-parallel line – 
> because it effectively alters the characteristic curve of the water supply at 
> that location.  On the other hand, it’s just a means of creating a safety 
> factor so who really cares.
>  
> If the water supply utilizes multiple flowing pumps, then it gets more 
> complicated since you need to consider altering flow and pressure.
>  
> If an engineer or AHJ wants some additional safety factor, then require a 
> cushion of a given pressure or percentage of the demand pressure and the 
> demand flow. But if you’ve done your homework and have identifies the a 
> reasonable ‘lowest pressure’, then you may not need to apply much safety 
> factor.
>  
> It’s all personal preference of the engineer/AHJ, but given the opportunity, 
> I do it my way….
>  
> -Mark
>  
> 
> <image9c32d3.JPG>     Mark Sornsin  
> Sr. Fire Protection Engineer
> Direct: 701-499-1391
> Cell: 701-526-8585
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of MFP Design, LLC
> Sent: Wednesday, August 08, 2018 4:04 PM
> To: [email protected]
> Subject: Flow Test Reductions
>  
> Lets assume a flow test of 100 static, 80 residual, 1500 gpm flow.  You are 
> required to reduce it by 10%.  Is the reduced flow test 90 / 70 / 1500 or 
> 90/72/1500?
>  
> I’ve always done it the first way because that keeps parallel lines.  
> However, I’ve run into more than a few people doing it the 2nd way lately.  
> Doing that has differing slopes and the lines would intersect.  The 
> theoretical reduction could actually have a higher pressure at a given flow 
> with #2 since it is a flatter curve.
>  
> <image002.jpg>
> Travis Mack, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>  
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>  
> “The bitterness of poor quality remains long after the sweetness of low price 
> is forgotten.”
>  
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to