NFPA 20 has never mandated jockey pumps. Back in the cycle for the development of the 1999 edition, in response to Proposal 20-36, the Committee Statement confirmed that "A pressure maintenance pump is not required by the standard. ..."
For the 2016 edition, some text was added, for the first time, to clarify that pressure maintenance is required for pressure-actuated fire pumps, but a jockey pump is not necessarily required to accomplish the task. Section 4.26.1 (c) allows "Another approved means that is not the main fire pump". And again, the Committee Statement confirmed "... a pressure maintenance pump may not necessarily be required and that other forms of pressure maintenance may be used. ...". Larry Keeping From: Sprinklerforum <[email protected]> On Behalf Of Thomas Reinhardt Sent: August-29-18 5:15 PM To: [email protected] Subject: No Jockey Pump Hi group, Found a 50 yr. old fire pump at a business that didn't have a jockey pump. Am I missing something. Thanks Tom Reinhardt Fire Inspector/Plan Reviewer Skokie Fire Department 7424 Niles Center Road Skokie, IL 60077 Office: 847-982-5342 [email protected]<mailto:[email protected]>