So why do we use jockey pumps? Wouldn’t one of Mike H’s flow switches alway be cheaper?
Best. Bruce Verhei > On Aug 29, 2018, at 19:05, Larry Keeping <[email protected]> wrote: > > NFPA 20 has never mandated jockey pumps. > > Back in the cycle for the development of the 1999 edition, in response to > Proposal 20-36, the Committee Statement confirmed that “A pressure > maintenance pump is not required by the standard. …” > > For the 2016 edition, some text was added, for the first time, to clarify > that pressure maintenance is required for pressure-actuated fire pumps, but a > jockey pump is not necessarily required to accomplish the task. Section > 4.26.1 (c) allows “Another approved means that is not the main fire pump”. > And again, the Committee Statement confirmed “… a pressure maintenance pump > may not necessarily be required and that other forms of pressure maintenance > may be used. …”. > > Larry Keeping > > > > From: Sprinklerforum <[email protected]> On > Behalf Of Thomas Reinhardt > Sent: August-29-18 5:15 PM > To: [email protected] > Subject: No Jockey Pump > > Hi group, > Found a 50 yr. old fire pump at a business that didn’t have a jockey pump. Am > I missing something. Thanks > > Tom Reinhardt > Fire Inspector/Plan Reviewer > Skokie Fire Department > 7424 Niles Center Road > Skokie, IL 60077 > Office: 847-982-5342 > [email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org