So why do we use jockey pumps? Wouldn’t one of Mike H’s flow switches alway be 
cheaper?

Best.

Bruce Verhei 

> On Aug 29, 2018, at 19:05, Larry Keeping <[email protected]> wrote:
> 
> NFPA 20 has never mandated jockey pumps.
>  
> Back in the cycle for the development of the 1999 edition, in response to 
> Proposal 20-36, the Committee Statement confirmed that “A pressure 
> maintenance pump is not required by the standard. …”
>  
> For the 2016 edition, some text was added, for the first time, to clarify 
> that pressure maintenance is required for pressure-actuated fire pumps, but a 
> jockey pump is not necessarily required to  accomplish the task. Section 
> 4.26.1 (c) allows “Another approved means that is not the main fire pump”. 
> And again, the Committee Statement confirmed “… a pressure maintenance pump 
> may not necessarily be required and that other forms of pressure maintenance 
> may be used. …”.
>  
> Larry Keeping
>  
>  
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Thomas Reinhardt
> Sent: August-29-18 5:15 PM
> To: [email protected]
> Subject: No Jockey Pump
>  
> Hi group,
> Found a 50 yr. old fire pump at a business that didn’t have a jockey pump. Am 
> I missing something. Thanks
>  
> Tom Reinhardt
> Fire Inspector/Plan Reviewer
> Skokie Fire Department
> 7424 Niles Center Road
> Skokie, IL 60077
> Office: 847-982-5342
> [email protected]
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to