You are approaching it correctly. See Fig. A.7.10.1.2.1.1 and text of A.7.10.1.2.1.1 and A.7.10.1.2.3.
The foregoing is my opinion only and is not intended to represent the NFPA 14 Technical Committee, nor serve as an interpretation of the standard. Steve Leyton Protection Design & Consulting San Diego, CA From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Wednesday, September 19, 2018 12:09 PM To: [email protected] Cc: Dewayne Martinez Subject: multi-height standpipes I have a high rise which contains 3 standpipes. Two of them go up 25 stories and the third only 4 stories. When I calculate them do I pick up 2@ 250gpm on the most remote high standpipe followed by 250 on the remaining stairwells including the low one or just the two high ones? To complicate the matter even more the high standpipes would not have a pressure reducing hose valves in the calculation but the low standpipe would need one. Thanks, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 [email protected]<mailto:[email protected]> Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [A close up of a sign Description generated with high confidence]
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org