Thanks for the information.  I will do one set of calcs to size my PRV hose
valves from floors 1-4 with the 3 standpipes flowing a total of 1000gpm and
an additional set of calcs for floors 5-25 with 2-standpipes flowing a
total of 750gpm.



Dewayne Martinez

Fire Protection Design Manager



*TOTAL* *Mechanical*

*Building* *Integrity*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/



[image: A close up of a sign Description generated with high confidence]



*From:* Sprinklerforum <[email protected]> *On
Behalf Of *MFP Design, LLC
*Sent:* Wednesday, September 19, 2018 2:12 PM
*To:* [email protected]
*Subject:* RE: multi-height standpipes



*I believe this is spelled out in the NFPA 14 handbook.  You will need to
do 2 sets of calculations.  Where you only have 2 standpipes, you calculate
the 750 gpm.  When you get down to the level with 3 standpipes, you do
another calc that goes to 1000 gpm.*



[image: MFP_logo_F]

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]



http://www.mfpdesign.com
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>

https://www.facebook.com/pages/MFP-Design-LLC/92218417692
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>

Send large files to us via: https://www.hightail.com/u/MFPDesign
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

LinkedIn: https://www.linkedin.com/in/travismack
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>



*“**The bitterness of poor quality remains long after the sweetness of low
price is forgotten.”*



*From:* Sprinklerforum <[email protected]> *On
Behalf Of *Dewayne Martinez
*Sent:* Wednesday, September 19, 2018 12:09 PM
*To:* [email protected]
*Cc:* Dewayne Martinez <[email protected]>
*Subject:* multi-height standpipes



I have a high rise which contains 3 standpipes.  Two of them go up 25
stories and the third only 4 stories.  When I calculate them do I pick up 2@
250gpm on the most remote high standpipe followed by 250 on the remaining
stairwells including the low one or just the two high ones?  To complicate
the matter even more the high standpipes would not have a pressure reducing
hose valves in the calculation but the low standpipe would need one.

Thanks,



Dewayne Martinez

Fire Protection Design Manager



*TOTAL Mechanical*

*Building* *Integrity*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/



[image: A close up of a sign Description generated with high confidence]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to